Skip to content
608 Practice Test

Core

EPA 608 Core: the refrigeration cycle, pressure classes and leak checks

Where refrigerant is liquid or vapor as it moves round a system, where the cooling actually happens, how EPA sorts appliances into pressure classes, and which leak checks find a leak and which only show that one exists.

Four stops round the loop

Refrigerant cools by changing state. It absorbs heat when liquid boils into vapor, and gives heat away when vapor condenses back into liquid.

  • Compressor: takes in vapor and squeezes it to a higher pressure. It is built for vapor, not liquid.
  • Condenser: heat flows from the hot gas to the outside air, so the refrigerant turns into a liquid.
  • Receiver (on systems that have one): a vessel connected to the system that stores liquid refrigerant.
  • Evaporator: the liquid boils into vapor and absorbs heat from the air or product. This is where cooling happens.
  • Suction accumulator: sits before the compressor and keeps liquid from reaching the compressor suction.

Pressure classes

EPA groups appliances by the refrigerant's liquid saturation pressure at 104 °F. The class decides which certification type and which evacuation levels apply.

  • Low-pressure: below 45 psia. Examples: R-11, R-123, R-113, R-245fa (Type III).
  • Medium-pressure: 45 to 170 psia. Examples: R-114, R-124, R-12, R-134a, R-500 (Type II).
  • High-pressure: 170 to 355 psia. Examples: R-22, R-407A, R-407C, R-410A, R-502 (Type II).
  • Very high-pressure: critical temperature below 104 °F or above 355 psia. Examples: R-13, R-23, R-503, R-508A, R-508B (Type II).

Finding leaks

  • A leak inspection looks for where refrigerant is escaping. Methods include ultrasonic tests, gas-imaging cameras, bubble tests and leak detectors used as the maker says.
  • Some checks only show that a system is losing refrigerant, not where. Standing pressure or vacuum decay tests, sight glass checks, receiver levels, pressure checks and charging charts are in this group.
  • Those "is it leaking?" checks must be paired with a method that finds the location.
  • After a repair, verification tests can use soap bubbles, electronic or ultrasonic detectors, pressure or vacuum tests, fluorescent dye with a black light, infrared tests or handheld gas detectors.
  • Use dry nitrogen, never oxygen or compressed air, when pressurising a system for a leak test.

Common traps

  • Cooling happens in the evaporator, not the condenser; the condenser rejects heat.
  • R-134a is medium-pressure, not high-pressure, but still Type II work.
  • A falling pressure reading proves a leak exists but does not locate it; you still need a locating method.
  • Liquid should never enter the compressor; that is the accumulator's job to prevent.

Key terms

Evaporator
Where liquid refrigerant boils to vapor and absorbs heat; the cooling coil.
Condenser
Where hot refrigerant gas gives off heat and turns into liquid.
Compressor
Raises the pressure of refrigerant vapor and moves it round the system.
Receiver
A vessel that stores liquid refrigerant.
Suction accumulator
Keeps liquid refrigerant out of the compressor suction.
psia
Pounds per square inch absolute, the scale EPA uses for pressure classes.
Low-pressure appliance
Uses a refrigerant below 45 psia at 104 °F, such as R-123.
High-pressure appliance
Uses a refrigerant between 170 and 355 psia at 104 °F, such as R-410A.

Practise all key terms with flashcards

Try 3 questions on this topic

3 free questions here; 10 on this topic with a pass.

Question 1 of 3

Refrigeration cycle, gauges and leak detection

In which part of a refrigeration system does the liquid refrigerant boil into vapor and absorb heat, producing the cooling effect?

Refrigeration cycle, gauges and leak detection: questions with answers

Choose your answer first, then open "Show the answer".

  1. 1.In which part of a refrigeration system does the liquid refrigerant boil into vapor and absorb heat, producing the cooling effect?

    • ACondenser
    • BEvaporator
    • CCompressor
    • DReceiver
    Show the answer

    Answer: B Evaporator

    The evaporator vaporizes liquid refrigerant, and that change of state absorbs heat from the air or product around it. This is where cooling happens.

    Source: OSHA: Ammonia Refrigeration eTool, Glossary

  2. 2.What is the job of a suction accumulator?

    • AIt stores extra oil for the condenser
    • BIt meters liquid refrigerant into the evaporator coil
    • CIt keeps liquid out of the compressor suction
    • DIt removes air from the system
    Show the answer

    Answer: C It keeps liquid out of the compressor suction

    An accumulator, also called a suction accumulator, keeps liquid refrigerant out of the compressor suction so only vapor reaches the compressor.

    Source: OSHA: Ammonia Refrigeration eTool, Glossary

  3. 3.A low-pressure appliance uses a refrigerant whose liquid saturation pressure at 104 degrees F is:

    • ABetween 45 and 170 psia
    • BBetween 170 and 355 psia
    • CAbove 355 psia
    • DBelow 45 psia
    Show the answer

    Answer: D Below 45 psia

    Low-pressure appliances use refrigerants with a liquid saturation pressure below 45 psia at 104 degrees F, such as R-11, R-123, R-113 and R-245fa.

    Source: eCFR: 40 CFR 82.152, Definitions