100 free practice questions, grouped by topic, with the answer and an explanation behind each one. Original practice questions for Core, Type I, Type II and Type III, each answer explained and tied to 40 CFR Part 82. With a pass you get all 319.

Prefer a timed test? Take the free practice test.

Ozone depletion and refrigerant types

Choose your answer first, then open "Show the answer".

  1. 1.Which atom released from CFC and HCFC refrigerants is the one that destroys ozone high in the atmosphere?

    • AFluorine
    • BChlorine
    • CCarbon
    • DHydrogen
    Show the answer

    Answer: B Chlorine

    EPA explains that chlorine and bromine atoms destroy ozone when they reach it in the stratosphere. CFCs and HCFCs carry chlorine; HFCs do not.

    Source: EPA: Basic Ozone Layer Science

  2. 2.What is the most important job the ozone layer does for life on Earth?

    • AIt keeps oxygen from escaping into space
    • BIt traps heat and keeps winters mild
    • CIt absorbs much of the sun's UVB radiation
    • DIt produces rain over the oceans
    Show the answer

    Answer: C It absorbs much of the sun's UVB radiation

    The ozone layer absorbs part of the sun's ultraviolet light, most importantly UVB. UVB is linked to skin cancer, cataracts and harm to crops and sea life.

    Source: EPA: Basic Ozone Layer Science

  3. 3.Which type of refrigerant is R-22?

    • AAn HCFC
    • BA CFC
    • CAn HFC
    • DA hydrocarbon (HC)
    Show the answer

    Answer: A An HCFC

    EPA's Core test topics use three standard examples: R-12 (CFC), R-22 (HCFC) and R-134 (HFC). R-22 contains hydrogen as well as chlorine.

    Source: EPA: Section 608 Technician Certification, Test Topics

  4. 4.Why do HFC refrigerants such as R-410A have an ozone depletion potential of zero?

    • AThey are heavier than air and never rise
    • BThey contain no chlorine or bromine
    • CThey break down before leaving the system
    • DThey contain more fluorine than CFCs
    Show the answer

    Answer: B They contain no chlorine or bromine

    HFCs are made of hydrogen, fluorine and carbon only. With no chlorine or bromine they do not deplete ozone, though some have a high global warming potential.

    Source: EPA: Section 608 Technician Certification, Test Topics

  5. 5.Scientists have measured which effect of extra UVB from ozone depletion on ocean life?

    • AFaster growth of coral reefs
    • BLower production of phytoplankton
    • CFaster warming of the sea surface water
    • DMore fish eggs hatching
    Show the answer

    Answer: B Lower production of phytoplankton

    EPA reports a direct drop in phytoplankton production linked to ozone depletion. UVB also harms the early life stages of fish, shrimp and crab.

    Source: EPA: Health and Environmental Effects of Ozone Layer Depletion

Lesson: Ozone depletion and refrigerant types

Clean Air Act, Montreal Protocol and Section 608 rules

Choose your answer first, then open "Show the answer".

  1. 1.During a repair on an R-22 system, a technician knowingly lets the refrigerant escape into the air instead of recovering it. Under Section 608, this is:

    • ALegal if the system holds less than 50 pounds
    • BIllegal venting
    • CLegal if the release takes place outdoors
    • DLegal because R-22 is no longer produced
    Show the answer

    Answer: B Illegal venting

    The venting prohibition bans knowingly releasing refrigerant during service, repair, maintenance or disposal. The size of the system and the place do not matter.

    Source: eCFR: 40 CFR 82.154, Prohibitions

  2. 2.A household freezer reaches a scrap metal yard with its refrigerant charge still inside. Who is responsible for making sure the refrigerant is recovered before final disposal?

    • AThe company that built the freezer
    • BThe original buyer only
    • CThe scrap yard (final processor)
    • DNo one, because small appliances are exempt
    Show the answer

    Answer: C The scrap yard (final processor)

    For equipment that is thrown away with its charge still inside, the last link in the chain, such as a scrap recycler or landfill, must make sure the refrigerant is recovered.

    Source: EPA: Stationary Refrigeration Safe Disposal Requirements

  3. 3.Which refrigerant sale is allowed to an uncertified buyer?

    • AA 2 lb or smaller MVAC can with a self-sealing valve
    • BA 25 lb cylinder of R-410A for a home heat pump
    • CA 30 lb cylinder of R-22 for a window air conditioner
    • DA 10 lb cylinder of R-134a for a chiller
    Show the answer

    Answer: A A 2 lb or smaller MVAC can with a self-sealing valve

    Small cans of non-exempt MVAC refrigerant, holding two pounds or less with a unique fitting and a self-sealing valve, may still be sold to uncertified people for their own vehicles.

    Source: EPA: Refrigerant Sales Restriction

  4. 4.Under Section 608, when may an uncertified apprentice connect gauges and recover refrigerant?

    • ANever; apprentices must pass the test first
    • BWhenever their employer gives written permission
    • COnly on systems holding less than 5 pounds
    • DUnder close, continual watch of a certified tech
    Show the answer

    Answer: D Under close, continual watch of a certified tech

    Apprentices are exempt from certification as long as a certified technician closely and continually supervises them. Both share responsibility for following the rules.

    Source: EPA: Types of Section 608 Technician Certification

  5. 5.From which year has production and import of HCFC-22 (R-22) been fully banned in the United States?

    • A2010
    • B2020
    • C2030
    • D1996
    Show the answer

    Answer: B 2020

    EPA's HCFC schedule ended production and import of HCFC-22 and HCFC-142b in 2020. Since 2010 R-22 could only be made for equipment built before January 1, 2010. R-22 can still be used to service existing equipment.

    Source: EPA: Phaseout of Class II Ozone-Depleting Substances

  6. 6.What does the Montreal Protocol do?

    • AIt certifies technicians in the United States
    • BIt sets the leak rates for supermarket systems
    • CIt sets the electrical safety codes for HVAC work in the U.S.
    • DIt phases out ozone-depleting substances worldwide
    Show the answer

    Answer: D It phases out ozone-depleting substances worldwide

    The Montreal Protocol is the international treaty that is gradually ending the production and consumption of ozone-depleting substances. The United States signed it in 1987.

    Source: EPA: International Actions, The Montreal Protocol

  7. 7.Which equipment is outside the Section 608 stationary refrigeration rules and handled under a separate program?

    • AMotor vehicle air conditioners
    • BHousehold refrigerators
    • CSupermarket display cases
    • DRooftop packaged air conditioners
    Show the answer

    Answer: A Motor vehicle air conditioners

    EPA's test topics describe the covered equipment as all air-conditioning and refrigeration equipment except motor vehicle air conditioners, which fall under Section 609.

    Source: EPA: Section 608 Technician Certification, Test Topics

Lesson: Clean Air Act, Montreal Protocol and Section 608 rules

Substitute refrigerants, oils and the HFC phase-down

Choose your answer first, then open "Show the answer".

  1. 1.A customer wants a replacement refrigerant that can simply be added to an old R-22 system with no other changes. What should the technician know?

    • AAny HFC can be mixed with the remaining R-22
    • BR-410A is a drop-in for R-22
    • CAny refrigerant with the same colour cylinder will work
    • DNo true drop-in exists; system changes may be needed
    Show the answer

    Answer: D No true drop-in exists; system changes may be needed

    EPA's Core topics include the absence of drop-in replacements. Converting to another refrigerant is a retrofit and may need new oil, seals, filters or other parts.

    Source: EPA: Section 608 Technician Certification, Test Topics

  2. 2.EPA's Core topics pair which lubricant with HCFC refrigerants such as R-22?

    • AEster
    • BAlkylbenzene
    • CGlycol antifreeze
    • DSilicone grease
    Show the answer

    Answer: B Alkylbenzene

    Substitutes and older refrigerants often need different oils. EPA's list pairs esters with R-134 and alkylbenzenes with HCFCs.

    Source: EPA: Section 608 Technician Certification, Test Topics

  3. 3.What is "fractionation" in a refrigerant blend?

    • AThe blend freezing inside the evaporator
    • BOil separating from the refrigerant in the compressor
    • CThe parts of a blend leaking at different rates
    • DThe blend turning into a single pure refrigerant
    Show the answer

    Answer: C The parts of a blend leaking at different rates

    Fractionation is the tendency of the different components of a blend to leak at different rates. After a leak, the refrigerant left in the system may no longer have the right mix.

    Source: EPA: Section 608 Technician Certification, Test Topics

Lesson: Substitute refrigerants, oils and the HFC phase-down

Refrigeration cycle, gauges and leak detection

Choose your answer first, then open "Show the answer".

  1. 1.In which part of a refrigeration system does the liquid refrigerant boil into vapor and absorb heat, producing the cooling effect?

    • ACondenser
    • BEvaporator
    • CCompressor
    • DReceiver
    Show the answer

    Answer: B Evaporator

    The evaporator vaporizes liquid refrigerant, and that change of state absorbs heat from the air or product around it. This is where cooling happens.

    Source: OSHA: Ammonia Refrigeration eTool, Glossary

  2. 2.What is the job of a suction accumulator?

    • AIt stores extra oil for the condenser
    • BIt meters liquid refrigerant into the evaporator coil
    • CIt keeps liquid out of the compressor suction
    • DIt removes air from the system
    Show the answer

    Answer: C It keeps liquid out of the compressor suction

    An accumulator, also called a suction accumulator, keeps liquid refrigerant out of the compressor suction so only vapor reaches the compressor.

    Source: OSHA: Ammonia Refrigeration eTool, Glossary

  3. 3.A low-pressure appliance uses a refrigerant whose liquid saturation pressure at 104 degrees F is:

    • ABetween 45 and 170 psia
    • BBetween 170 and 355 psia
    • CAbove 355 psia
    • DBelow 45 psia
    Show the answer

    Answer: D Below 45 psia

    Low-pressure appliances use refrigerants with a liquid saturation pressure below 45 psia at 104 degrees F, such as R-11, R-123, R-113 and R-245fa.

    Source: eCFR: 40 CFR 82.152, Definitions

Lesson: Refrigeration cycle, gauges and leak detection

Recover, recycle, reclaim and evacuation

Choose your answer first, then open "Show the answer".

  1. 1.What does "recover" mean under Section 608?

    • AClean refrigerant with filter-driers for reuse by the same owner
    • BReprocess refrigerant to AHRI 700 purity and test it
    • CRemove it and store it in a container, with no testing required
    • DDestroy refrigerant at an EPA-approved destruction facility
    Show the answer

    Answer: C Remove it and store it in a container, with no testing required

    Recovering means taking refrigerant out of a system, in whatever condition, and putting it in a separate container. No testing or cleaning is required.

    Source: eCFR: 40 CFR 82.152, Definitions

  2. 2.What does "reclaim" mean?

    • APump refrigerant into the receiver during service
    • BRemove refrigerant and store it in a cylinder
    • CClean refrigerant with a filter-drier at the job site for reuse
    • DReprocess it to AHRI 700-2016 specs and verify by analysis
    Show the answer

    Answer: D Reprocess it to AHRI 700-2016 specs and verify by analysis

    To reclaim is to reprocess recovered refrigerant to all applicable specifications in Appendix A (based on AHRI Standard 700-2016) and verify it with the prescribed analysis.

    Source: eCFR: 40 CFR 82.152, Definitions

  3. 3.What is self-contained recovery equipment?

    • AEquipment that uses the appliance's compressor to push out refrigerant
    • BEquipment that works without help from the appliance's parts
    • CA cylinder that seals itself when disconnected
    • DEquipment that only works on small appliances
    Show the answer

    Answer: B Equipment that works without help from the appliance's parts

    Self-contained equipment removes refrigerant on its own. System-dependent equipment needs the appliance's components, such as its compressor, to do the work.

    Source: eCFR: 40 CFR 82.152, Definitions

  4. 4.Which of these is listed by EPA as a factor that affects how fast refrigerant recovery goes?

    • AThe colour of the recovery cylinder
    • BThe brand of refrigerant
    • CHose length and diameter
    • DThe day of the week
    Show the answer

    Answer: C Hose length and diameter

    EPA's Core topics list ambient temperature, the size of the recovery equipment and hose length and diameter as factors in recovery speed. Short, wide hoses flow better than long, narrow ones.

    Source: EPA: Section 608 Technician Certification, Test Topics

Lesson: Recover, recycle, reclaim and evacuation

Safety, cylinders and shipping

Choose your answer first, then open "Show the answer".

  1. 1.A large R-22 leak happens in a small basement equipment room. Why is this especially dangerous?

    • AR-22 vapor rises quickly and escapes through the ceiling
    • BR-22 burns easily at room temperature
    • CR-22 turns into ozone when it leaks
    • DIts heavy vapor collects low and displaces oxygen
    Show the answer

    Answer: D Its heavy vapor collects low and displaces oxygen

    NIOSH gives R-22 a relative gas density of 3.11, so it is heavier than air and can collect in low spaces, displacing oxygen. Asphyxia (suffocation) is one of the listed effects.

    Source: CDC/NIOSH: Pocket Guide to Chemical Hazards, Chlorodifluoromethane (R-22)

  2. 2.Liquid refrigerant can cause frostbite. What basic protective equipment should a technician wear when connecting hoses and handling refrigerant?

    • AGloves and safety goggles
    • BA dust mask only
    • CHearing protection only
    • DNo equipment if the system is switched off
    Show the answer

    Answer: A Gloves and safety goggles

    EPA's Core topics list gloves and goggles as personal protective equipment, with self-contained breathing apparatus (SCBA) in extreme cases. NIOSH lists frostbite of skin and eyes from liquid refrigerant.

    Source: EPA: Section 608 Technician Certification, Test Topics

  3. 3.Which gas should be used to pressurise a system for a leak test?

    • AOxygen
    • BCompressed shop air
    • CAcetylene
    • DDry nitrogen
    Show the answer

    Answer: D Dry nitrogen

    EPA's Core topics call for nitrogen rather than oxygen or compressed air when leak testing.

    Source: EPA: Section 608 Technician Certification, Test Topics

Lesson: Safety, cylinders and shipping

Small appliances: definition and recovery requirements

Choose your answer first, then open "Show the answer".

  1. 1.Under the Section 608 rules, what is the most refrigerant a factory-sealed appliance can hold and still count as a small appliance?

    • A15 pounds
    • B5 pounds
    • C2 pounds
    • D50 pounds
    Show the answer

    Answer: B 5 pounds

    40 CFR 82.152 sets the limit: the appliance must be completely built, charged and sealed at the factory, holding no more than 5 pounds of refrigerant.

    Source: eCFR: 40 CFR 82.152, Definitions

  2. 2.A hotel has packaged terminal air heat pumps (PTACs) under each window, each sealed at the factory with 3 pounds of refrigerant. How does the rule treat them?

    • AAs high-pressure appliances that need Type II work
    • BAs MVAC-like appliances
    • CAs equipment outside the Section 608 rules
    • DAs small appliances
    Show the answer

    Answer: D As small appliances

    The small-appliance definition lists room air conditioners, including window units, portable units and packaged terminal air heat pumps, when they are factory sealed with 5 pounds or less.

    Source: eCFR: 40 CFR 82.152, Definitions

  3. 3.Using a recovery machine made in 2019 on a refrigerator whose compressor runs, what percentage of the refrigerant must be recovered?

    • A80 percent
    • B85 percent
    • C90 percent
    • D100 percent
    Show the answer

    Answer: C 90 percent

    40 CFR 82.156(b)(2) requires 90 percent recovery when the equipment was made on or after November 15, 1993 and the appliance compressor works. Pulling 4 inches of mercury vacuum also meets the rule.

    Source: eCFR: 40 CFR 82.156, Proper evacuation of refrigerant from appliances

  4. 4.A freezer's compressor is seized. The technician has a recovery unit made in 2021. What is the required recovery level?

    • A90 percent
    • B80 percent
    • C75 percent
    • D4 psig
    Show the answer

    Answer: B 80 percent

    Under 40 CFR 82.156(b)(2), equipment made on or after November 15, 1993 must recover 80 percent when the appliance compressor is not working (or reach 4 inches of mercury vacuum).

    Source: eCFR: 40 CFR 82.156, Proper evacuation of refrigerant from appliances

  5. 5.Which organizations has EPA approved to certify refrigerant recovery and recycling equipment?

    • AAHRI and UL
    • BASHRAE and OSHA
    • CDOT and NIST
    • DANSI and the EPA regional offices
    Show the answer

    Answer: A AHRI and UL

    EPA approved two testing bodies to certify recovery and recycling equipment: AHRI (the Air-Conditioning, Heating, and Refrigeration Institute) and UL (Underwriters Laboratories).

    Source: US EPA: Refrigerant recovery and recycling equipment certification

  6. 6.Jordan passed Type I by mail and later passes Type II and Type III at a proctored site. Does this give Universal certification?

    • ANo, a mail-in Type I test cannot count toward Universal
    • BYes, any three passed types make Universal
    • CYes, if all three were passed within one year
    • DNo, Universal can only be earned in one single sitting
    Show the answer

    Answer: A No, a mail-in Type I test cannot count toward Universal

    Appendix D says mail-in Type I tests cannot be used toward Universal certification. Universal may combine separate Type I, II and III passes only when they are closed-book tests.

    Source: eCFR: 40 CFR 82, Subpart F, Appendix D (standards for technician certifying programs)

  7. 7.How many questions does a Type I certification test contain under Appendix D?

    • A50 questions, all on Type I topics
    • B25 questions, all on Type I topics
    • C100 questions from all groups
    • D25 Core plus 25 Type I questions
    Show the answer

    Answer: D 25 Core plus 25 Type I questions

    Appendix D says each test includes 25 questions from Group 1 (Core) and 25 from each technical group taken, so a Type I test has 50 questions.

    Source: eCFR: 40 CFR 82, Subpart F, Appendix D (standards for technician certifying programs)

  8. 8.Which task on a window air conditioner can only be done by a certified technician (or a supervised apprentice)?

    • APainting the cabinet and front grille
    • BReplacing the power cord
    • CAttaching gauges to read pressure
    • DTightening the mounting bolts
    Show the answer

    Answer: C Attaching gauges to read pressure

    EPA lists attaching and detaching hoses and gauges to measure pressure as an activity that makes someone a technician. Painting, rewiring and tightening bolts are not.

    Source: US EPA: Section 608 technician certification requirements

  9. 9.A water cooler contains R-134a, an HFC that does not harm the ozone layer. Do the recovery rules for small appliances apply to it?

    • ANo, they cover only ozone-depleting CFCs and HCFCs
    • BYes, since January 1, 2018
    • CNo, because HFCs may always be vented
    • DOnly if the cooler holds more than 1 pound
    Show the answer

    Answer: B Yes, since January 1, 2018

    Since January 1, 2018, 40 CFR 82.156 covers appliances holding ozone-depleting refrigerants and also non-exempt substitutes, so an HFC like R-134a in a water cooler is included.

    Source: eCFR: 40 CFR 82.156, Proper evacuation of refrigerant from appliances

  10. 10.A customer drops off a refrigerator with a sticker saying the refrigerant has been removed. Is the sticker enough for the scrap yard?

    • AYes, if the sticker is dated
    • BYes, if the sticker shows a technician's name
    • CYes, for refrigerators but not for freezers
    • DNo, EPA does not accept a sticker as verification
    Show the answer

    Answer: D No, EPA does not accept a sticker as verification

    EPA does not require or accept a sticker as proof of recovery. The final disposer needs a signed statement or a contract with the supplier.

    Source: US EPA: Stationary refrigeration safe disposal requirements

Lesson: Small appliances: definition and recovery requirements

Small appliances: recovery techniques

Choose your answer first, then open "Show the answer".

  1. 1.Which two readings does EPA expect a Type I technician to use to identify a refrigerant and check for noncondensables?

    • AWeight and color
    • BPressure and temperature
    • CVoltage and current
    • DOil level and odor
    Show the answer

    Answer: B Pressure and temperature

    EPA's Type I test topics include using pressure and temperature to identify refrigerants and to detect noncondensables.

    Source: US EPA: Section 608 technician certification test topics

  2. 2.A recovery cylinder holds liquid R-134a at a steady room temperature, but its pressure is higher than the chart value for R-134a at that temperature. What does this most likely mean?

    • AAir or other noncondensables are present
    • BThe cylinder is less than half full of liquid
    • CThe refrigerant inside is colder than the room
    • DThe cylinder valve is only partly open
    Show the answer

    Answer: A Air or other noncondensables are present

    Comparing pressure with temperature is how technicians detect noncondensables. A reading above the expected value for that refrigerant suggests air or other gases that do not condense.

    Source: US EPA: Section 608 technician certification test topics

  3. 3.When a vacuum pump is used to help passive recovery from a small appliance, what kind of container should collect the refrigerant?

    • AA disposable refrigerant cylinder
    • BA nitrogen cylinder
    • CA non-pressurized recovery container
    • DA pressurized storage tank filled to 80 percent
    Show the answer

    Answer: C A non-pressurized recovery container

    EPA lists using a vacuum pump with a non-pressurized recovery container as a passive recovery method for small appliances whose compressor does not work.

    Source: US EPA: Section 608 technician certification test topics

  4. 4.What is self-contained recovery equipment?

    • AA recovery bag fitted to the process stub of the appliance
    • BEquipment that works without help from the appliance's parts
    • CEquipment that only works when the appliance compressor runs
    • DA recovery cylinder with a built-in scale
    Show the answer

    Answer: B Equipment that works without help from the appliance's parts

    40 CFR 82.152 defines self-contained recovery equipment as equipment able to remove refrigerant without the help of components contained in the appliance.

    Source: eCFR: 40 CFR 82.152, Definitions

  5. 5.Ahmed recovers refrigerant from a customer's ice maker to repair it. May he charge that same refrigerant back into the same ice maker?

    • ANo, it must be sent for reclaim first
    • BNo, recovered refrigerant must always be destroyed
    • CYes, without recycling or reclaim
    • DOnly if it is tested by a laboratory first
    Show the answer

    Answer: C Yes, without recycling or reclaim

    40 CFR 82.156(h) allows recovered refrigerant to go back into the appliance it came from, or another appliance of the same owner, without recycling or reclaim (MVACs excepted).

    Source: eCFR: 40 CFR 82.156, Proper evacuation of refrigerant from appliances

  6. 6.Why are small-appliance recovery devices tested both with the test stand compressor running and with it off?

    • ATo check the compressor's electrical safety
    • BTo measure how fast the stand cools
    • CTo find the recovery efficiency in either condition
    • DTo test the device's oil level
    Show the answer

    Answer: C To find the recovery efficiency in either condition

    Appendix C runs separate tests with the test stand compressor on and off so the device's recovery efficiency is known under either condition.

    Source: eCFR: 40 CFR 82, Subpart F, Appendix C (testing recovery devices for small appliances)

  7. 7.A window unit holds 20 ounces and its compressor runs. With recovery equipment made in 2015, how much must be recovered (unless 4 inches of vacuum is reached)?

    • A16 ounces
    • B19 ounces
    • C18 ounces
    • D15 ounces
    Show the answer

    Answer: C 18 ounces

    Equipment made on or after November 15, 1993 must recover 90 percent when the appliance compressor works: 0.90 x 20 = 18 ounces.

    Source: eCFR: 40 CFR 82.156, Proper evacuation of refrigerant from appliances

  8. 8.How can a technician tell that a recovery machine has been certified for small appliances?

    • ABy its yellow and gray paint
    • BBy the manufacturer's warranty card
    • CBy a sticker from the refrigerant wholesaler
    • DBy its certification label
    Show the answer

    Answer: D By its certification label

    Certified recovery equipment carries a permanent label saying it was certified by AHRI or UL to meet EPA's minimum requirements for the stated category of appliance.

    Source: US EPA: Refrigerant recovery and recycling equipment certification

  9. 9.Which change would usually speed up recovery from a small appliance?

    • AUsing shorter hoses with a larger inside diameter
    • BUsing longer hoses
    • CUsing narrower hoses
    • DRecovering on the coldest day possible
    Show the answer

    Answer: A Using shorter hoses with a larger inside diameter

    EPA's test topics list ambient temperature, the size of the recovery equipment, and hose length and diameter as factors affecting recovery speed.

    Source: US EPA: Section 608 technician certification test topics

  10. 10.Under 40 CFR 82.152, what does it mean to "recover" refrigerant?

    • ATo clean it with filter-driers for reuse by the same owner
    • BTo remove it and store it in an outside container, in any condition
    • CTo reprocess it to AHRI 700 purity and verify that by analysis
    • DTo release it slowly outdoors
    Show the answer

    Answer: B To remove it and store it in an outside container, in any condition

    40 CFR 82.152 defines recovering as taking refrigerant out of an appliance, whatever its condition, and holding it in an external container, with no need to test or process it.

    Source: eCFR: 40 CFR 82.152, Definitions

Lesson: Small appliances: recovery techniques

Small appliances: safety and refrigerants

Choose your answer first, then open "Show the answer".

  1. 1.R-12 vapor from a leaking freezer is drawn into a torch flame. Which highly toxic gas can form?

    • ACarbon dioxide
    • BPhosgene
    • CNitrogen
    • DMethane
    Show the answer

    Answer: B Phosgene

    PubChem's decomposition data for R-12 says that when heated to decomposition it gives off highly toxic phosgene, hydrogen chloride and hydrogen fluoride.

    Source: PubChem (NIH): Dichlorodifluoromethane (R-12), Decomposition

  2. 2.R-134a has no chlorine. Is it safe to let its vapor pass over a flame or red-hot metal?

    • AYes, because only refrigerants that contain chlorine decompose
    • BYes, R-134a is a hydrocarbon
    • CNo, it can also decompose into toxic products
    • DYes, if the room is air conditioned
    Show the answer

    Answer: C No, it can also decompose into toxic products

    PubChem's R-134a data says all fluorocarbons undergo thermal decomposition in a flame or on red-hot metal, and R-134a gives off toxic fluoride vapors when heated.

    Source: PubChem (NIH): 1,1,1,2-Tetrafluoroethane (R-134a), Decomposition

  3. 3.According to EPA's SNAP use conditions, who should service refrigerators and freezers that contain hydrocarbon refrigerants?

    • AAny person, because the charge in these units is small
    • BOnly technicians trained in flammable refrigerants
    • CAny Type II technician
    • DOnly the original manufacturer
    Show the answer

    Answer: B Only technicians trained in flammable refrigerants

    EPA's SNAP use conditions say these refrigerators and freezers should be serviced only by technicians who have had specific training in flammable refrigerants.

    Source: eCFR: 40 CFR 82, Subpart G, Appendix R (SNAP use conditions for hydrocarbon refrigerants)

  4. 4.While hydrocarbon refrigerators are stored, the refrigerant in the air rises above 25 percent of its lower flammability limit (LFL). What should happen?

    • AEvacuate the space and ventilate it before re-entry
    • BWork can continue as long as no one in the room smokes
    • CThe refrigerators should be switched on to use up the gas
    • DNothing, because one-fourth of the limit cannot burn
    Show the answer

    Answer: A Evacuate the space and ventilate it before re-entry

    EPA's SNAP use conditions say that when refrigerant in the air goes above a quarter of the LFL, people should leave the space and return only after it has been ventilated.

    Source: eCFR: 40 CFR 82, Subpart G, Appendix R (SNAP use conditions for hydrocarbon refrigerants)

  5. 5.A dehumidifier releases its charge in a small closed room. Besides frostbite, what breathing risk does refrigerant vapor create?

    • ACarbon monoxide poisoning
    • BToo much oxygen in the air
    • COxygen deprivation
    • DRadiation exposure
    Show the answer

    Answer: C Oxygen deprivation

    EPA's test topics list oxygen deprivation, cardiac effects, frostbite and long-term hazards as risks of refrigerant exposure.

    Source: US EPA: Section 608 technician certification test topics

Lesson: Small appliances: safety and refrigerants

High-pressure: leak detection and leak repair

Choose your answer first, then open "Show the answer".

  1. 1.During a walk-through, Dana sees an oily film on a valve and the piping around it on a compressor rack. What should she do next?

    • APinpoint the leak there with bubbles or an electronic detector
    • BWipe the oil off the valve and piping, then close out the call
    • CAdd refrigerant until the sight glass runs clear again
    • DIgnore it, because an oil film is not a refrigerant leak
    Show the answer

    Answer: A Pinpoint the leak there with bubbles or an electronic detector

    Traces of oil are a common sign of a refrigerant leak, especially on hermetic systems. EPA's GreenChill guide says that where oil seepage is seen, a bubble test or electronic detector should be used to find the exact spot.

    Source: US EPA GreenChill: Best Practices Guideline, Commercial Refrigeration Leak Prevention & Repairs (2011)

  2. 2.An electronic leak detector cannot sense pure nitrogen. If some refrigerant is needed for the test, which choice does EPA rank higher than using pure refrigerant?

    • ANitrogen with a trace amount of R-22
    • BA full charge of R-22 with no nitrogen
    • CCompressed air with a trace amount of R-22
    • DOxygen with a trace amount of R-22
    Show the answer

    Answer: A Nitrogen with a trace amount of R-22

    EPA's order is nitrogen alone first, then nitrogen with a trace of HCFC-22, and pure refrigerant last. The trace lets an electronic detector find the leak while using very little refrigerant.

    Source: US EPA: Section 608 Technician Certification Test Topics (Core and Type 2)

  3. 3.Under 40 CFR 82.157, the leak repair rules for ozone-depleting refrigerants such as R-22 apply to appliances with a full charge of at least how much refrigerant?

    • A5 pounds
    • B50 pounds
    • C15 pounds
    • D200 pounds
    Show the answer

    Answer: B 50 pounds

    Since April 10, 2020, 40 CFR 82.157 covers only appliances whose full charge is 50 pounds or more of an ozone-depleting (class I or II) refrigerant, such as R-22.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  4. 4.An office building has an R-22 chiller with 400 pounds of refrigerant. Above what leak rate must it be repaired?

    • A15 percent
    • B10 percent
    • C20 percent
    • D30 percent
    Show the answer

    Answer: B 10 percent

    A chiller that cools occupied space is comfort cooling. 40 CFR 82.157 sets a 10 percent trigger for comfort cooling and other appliances with 50 or more pounds.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  5. 5.A city ice rink uses an R-22 system with 800 pounds of refrigerant. Which trigger leak rate applies?

    • A30 percent, as ice rinks are industrial process refrigeration
    • B10 percent, because the rink is a public building used by people
    • C20 percent, because the rink is a form of cold storage
    • D35 percent, because the system holds more than 500 pounds
    Show the answer

    Answer: A 30 percent, as ice rinks are industrial process refrigeration

    The definition of industrial process refrigeration in 82.152 includes industrial ice machines, power generation cooling and ice rinks, so the 30 percent trigger applies.

    Source: eCFR: 40 CFR 82.152 Definitions

  6. 6.Using the rolling average method: a chiller has a full charge of 150 pounds. Over the past 365 days, 12, 6 and 12 pounds were added. What is the leak rate?

    • A8 percent
    • B20 percent
    • C10 percent
    • D30 percent
    Show the answer

    Answer: B 20 percent

    The rolling average method sums the pounds added over the previous 365 days and divides by the full charge: 30 / 150 = 0.2, or 20 percent.

    Source: eCFR: 40 CFR 82.152 Definitions

  7. 7.An R-22 commercial refrigeration system is found to exceed its trigger rate when refrigerant is added. With no process shutdown needed, how long does the owner have to identify and repair the leaks?

    • A10 days
    • B30 days
    • C120 days
    • DOne year
    Show the answer

    Answer: B 30 days

    Under 82.157(d), leaks must be found and fixed within 30 days of adding refrigerant to an appliance over its trigger rate. Only an industrial process shutdown allows 120 days.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  8. 8.A leaking coil on a large R-22 system was replaced, which meant evacuating that part of the system. When must the initial verification test be done?

    • AAfter the system is recharged and running normally
    • BWithin 10 days after the recharge
    • CBefore any refrigerant is added back
    • DAt the next yearly inspection
    Show the answer

    Answer: C Before any refrigerant is added back

    For repairs that required evacuating the appliance or part of it, the initial verification test must be done before any refrigerant is added.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  9. 9.An owner sends EPA a complete, on-time request for more time to repair leaks under 82.157(f). When is the extension approved?

    • AIt is approved unless EPA tells the owner otherwise
    • BOnly after EPA sends the owner a written approval letter
    • COnly if EPA has not replied within 60 days of receipt
    • DOnly after the state environmental agency signs it
    Show the answer

    Answer: A It is approved unless EPA tells the owner otherwise

    Under 82.157(f), an extension request that meets the conditions is considered approved unless EPA notifies the owner otherwise.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  10. 10.A technician adds R-22 to a customer's 90-pound appliance. What must the technician give the owner when the job ends?

    • ANothing, because only the owner keeps the leak repair records
    • BA service record showing the amount and type of refrigerant added
    • COnly a copy of the technician's Section 608 certification card
    • DNothing to the owner; a leak rate report goes straight to EPA
    Show the answer

    Answer: B A service record showing the amount and type of refrigerant added

    Under 82.157(b), persons adding or removing refrigerant must give the owner documentation at the end of the service, including the amount and type of refrigerant added, so the owner can calculate the leak rate.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

Lesson: High-pressure: leak detection and leak repair

High-pressure: recovery requirements and techniques

Choose your answer first, then open "Show the answer".

  1. 1.How do EPA's rules define a high-pressure appliance?

    • AIts refrigerant's liquid saturation pressure is under 45 psia at 104 °F
    • BIts refrigerant's liquid saturation pressure is 45 to 170 psia at 104 °F
    • CIts refrigerant's liquid saturation pressure is 170 to 355 psia at 104 °F
    • DIts refrigerant has a critical temperature below 104 °F
    Show the answer

    Answer: C Its refrigerant's liquid saturation pressure is 170 to 355 psia at 104 °F

    40 CFR 82.152 classes an appliance as high-pressure when, at 104 °F, its refrigerant's liquid saturation pressure is from 170 to 355 psia.

    Source: eCFR: 40 CFR 82.152 Definitions

  2. 2.Under 40 CFR 82.161, which certification covers a technician who services an R-134a chiller, a medium-pressure appliance?

    • AType II
    • BType I
    • CType III
    • DNo certification, since R-134a is not ozone-depleting
    Show the answer

    Answer: A Type II

    40 CFR 82.161 puts medium-pressure appliances in Type II, together with high- and very high-pressure ones (small appliances and vehicle AC are excluded).

    Source: eCFR: 40 CFR 82.161 Technician certification

  3. 3.An R-22 chiller holds 350 pounds. Using recovery equipment made in 2018, to what level must it be evacuated before a major repair?

    • A10 inches of mercury vacuum
    • B0 inches of mercury vacuum
    • C4 inches of mercury vacuum
    • D25 mm of mercury absolute
    Show the answer

    Answer: A 10 inches of mercury vacuum

    Table 1 sets 10 inches of mercury vacuum for high-pressure appliances with 200 pounds or more when using equipment made on or after 15 November 1993.

    Source: US EPA: Stationary Refrigeration Service Practice Requirements

  4. 4.Must a technician always evacuate the whole appliance before opening it?

    • ANo, only the part being serviced, if isolated to a system receiver
    • BYes, the whole appliance must always be evacuated, every time
    • CNo, the technician may close the service valves and open the part
    • DYes, unless the system holds less than 200 pounds of refrigerant
    Show the answer

    Answer: A No, only the part being serviced, if isolated to a system receiver

    82.156(a) allows evacuating just the section being worked on, as long as its refrigerant can be held in a system receiver.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  5. 5.A 250-pound R-22 chiller with no leaks is being scrapped, using a recovery machine made in 2020. Can the technician stop at 0 psig, as for a non-major repair?

    • AYes; 0 psig is enough for any job on a high-pressure system
    • BYes; disposal needs no set level once the unit is shut down
    • CNo; it must reach the Table 1 level of 10 inches Hg
    • DNo; disposal needs a deep vacuum of 500 microns or lower
    Show the answer

    Answer: C No; it must reach the Table 1 level of 10 inches Hg

    82.156(a) requires technicians to evacuate refrigerant, including all liquid, to the Table 1 levels before opening or disposing of these appliances. For 200 pounds or more with post-1993 equipment, that is 10 inches Hg.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  6. 6.A rooftop unit holds 25 pounds of R-22. May the technician use system-dependent (passive) recovery equipment on it?

    • AYes, if the compressor is working
    • BNo, unless it is a permanently attached pump-out unit
    • CYes, for any high-pressure appliance
    • DNo, because system-dependent equipment is allowed only on low-pressure chillers
    Show the answer

    Answer: B No, unless it is a permanently attached pump-out unit

    82.156(e) says system-dependent equipment may not be used on appliances with more than 15 pounds of refrigerant, unless it is permanently attached as a pump-out unit.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  7. 7.Before changing the compressor oil in an R-22 system, how low must the pressure be?

    • ANo higher than 0 psig
    • B10 inches of mercury vacuum
    • CNo higher than 15 psig
    • DNo higher than 5 psig
    Show the answer

    Answer: D No higher than 5 psig

    EPA treats an oil change above 5 psig as a violation, because the oil holds dissolved refrigerant. The oil may also be drained into a system receiver brought to 5 psig or less.

    Source: US EPA: Stationary Refrigeration Service Practice Requirements

  8. 8.Which hose setup gives the fastest recovery?

    • AShort hoses with a large inside diameter
    • BLong hoses with a small inside diameter
    • CLong hoses with a large inside diameter
    • DShort hoses with a small inside diameter
    Show the answer

    Answer: A Short hoses with a large inside diameter

    EPA lists hose length and diameter among the factors that affect recovery speed. Shorter, wider hoses give less restriction and faster recovery.

    Source: US EPA: Section 608 Technician Certification Test Topics (Core and Type 2)

  9. 9.Mia's recovery machine was last used on R-22. She now needs it for R-410A. What should she do first?

    • ANothing, because small amounts of R-22 left inside do not matter
    • BClear the R-22 out of the machine using the maker's steps
    • CRecover the R-410A into the same cylinder as the R-22
    • DRelease the R-22 left in the machine to the outside air
    Show the answer

    Answer: B Clear the R-22 out of the machine using the maker's steps

    EPA's topics cover the need to avoid mixing refrigerants and to reduce cross-contamination when a recovery machine is used with a new refrigerant. Recovery equipment must be used according to the manufacturer's directions.

    Source: US EPA: Section 608 Technician Certification Test Topics (Core and Type 2)

  10. 10.A technician recovers refrigerant to dispose of a 30-pound R-22 rooftop unit. For how long must the disposal records be kept?

    • AOne year
    • BThree years
    • CFive years
    • DNo records are needed under 50 pounds
    Show the answer

    Answer: B Three years

    When disposing of appliances that hold over 5 but under 50 pounds, technicians keep records of the company, location, date and refrigerant type for three years.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

Lesson: High-pressure: recovery requirements and techniques

High-pressure: safety, charging and disposal

Choose your answer first, then open "Show the answer".

  1. 1.A system has just been pulled into a deep vacuum. Why should the technician not energize the hermetic compressor?

    • ARunning it under vacuum can damage its motor
    • BIt will speed up the evacuation far too much
    • CIt is needed later to break the vacuum safely
    • DIt will make the vacuum gauge read wrongly
    Show the answer

    Answer: A Running it under vacuum can damage its motor

    EPA's Type 2 safety topics say you should not energize hermetic compressors under vacuum. Without refrigerant around the windings, the motor can be damaged.

    Source: US EPA: Section 608 Technician Certification Test Topics (Core and Type 2)

  2. 2.A gauge reads 100 psig. To use a chart in absolute pressure, what is the reading in psia?

    • A85.3 psia
    • B100 psia
    • C114.7 psia
    • D129.4 psia
    Show the answer

    Answer: C 114.7 psia

    To change pounds per square inch gauge to absolute, add 14.7: 100 + 14.7 = 114.7 psia.

    Source: US EPA: Section 608 Technician Certification Test Topics (Core and Type 2)

  3. 3.Which container may be used to hold recovered R-410A?

    • AAn empty disposable cylinder from a new R-410A purchase
    • BA DOT-approved gray recovery cylinder with a yellow top
    • CAny cylinder that once held the same refrigerant
    • DA nitrogen cylinder with its valve swapped out
    Show the answer

    Answer: B A DOT-approved gray recovery cylinder with a yellow top

    EPA's topics contrast reusable recovery cylinders, which must be DOT-approved and are yellow and gray, with disposable cylinders, which must never be refilled.

    Source: US EPA: Section 608 Technician Certification Test Topics (Core and Type 2)

  4. 4.During a leak check, a technician finds that a pressure relief valve on a rack has discharged. What does EPA's GreenChill guide advise?

    • AFix the cause, then replace the relief valve
    • BReset the valve and leave it in place
    • CPlug the valve outlet to stop any more loss
    • DAdd refrigerant and check the valve next month
    Show the answer

    Answer: A Fix the cause, then replace the relief valve

    GreenChill advises that a relief valve should never discharge in normal conditions. If it has, find and correct the cause and replace the valve, since it is designed for one release and may seep.

    Source: US EPA GreenChill: Best Practices Guideline, Commercial Refrigeration Leak Prevention & Repairs (2011)

  5. 5.Which list matches the kinds of risk that EPA names for refrigerants?

    • ARadiation, flammability, noise and vibration
    • BToxicity and radiation, but no physical hazards
    • CAsphyxiation only, since all refrigerants are inert
    • DToxicity, flammability, asphyxiation and physical hazards
    Show the answer

    Answer: D Toxicity, flammability, asphyxiation and physical hazards

    EPA's refrigerant safety page names four kinds of risk: toxicity, flammability, asphyxiation and physical hazards. Good design and safe work reduce them.

    Source: US EPA SNAP: Refrigerant Safety

Lesson: High-pressure: safety, charging and disposal

Low-pressure: leak detection and leak repair

Choose your answer first, then open "Show the answer".

  1. 1.A technician must raise the pressure inside an R-123 chiller to look for leaks. Which method comes first in the usual order of preference?

    • AHot water or a built-in heater such as Prevac
    • BDry nitrogen from a cylinder with a regulator and relief valve
    • CCompressed shop air, dried through a filter
    • DRefrigerant vapor mixed with air
    Show the answer

    Answer: A Hot water or a built-in heater such as Prevac

    For low-pressure systems the first choice is to warm the refrigerant: hot water through the tubes or a built-in heating/pressurization device. Heat raises the pressure without adding a gas that later has to be purged.

    Source: US EPA: Section 608 Technician Certification Test Topics, Type 3 (Low-pressure)

  2. 2.Why does a leak in a running R-123 chiller often let air in instead of letting refrigerant out?

    • AR-123 vapor is heavier than air, so it stays inside
    • BParts of it are below atmospheric pressure
    • CThe rupture disc holds refrigerant in and lets air pass
    • DThe purge unit seals small holes as it runs
    Show the answer

    Answer: B Parts of it are below atmospheric pressure

    Low-pressure refrigerants let sections of the chiller sit below atmospheric pressure, running or not. Where inside pressure is lower, a leak draws air and moisture in.

    Source: Trane: CenTraVac chillers Installation, Operation, and Maintenance (CVHE-SVX005E-EN, 2026)

  3. 3.A leak on an R-123 chiller is too small to find with nitrogen and soap. What does the maker's guide say to use?

    • AA mixture of refrigerant and air, which shows up well
    • BPure refrigerant vapor raised to 15 psig
    • COxygen, so the leak shows up faster
    • DA little trace gas carried in dry nitrogen
    Show the answer

    Answer: D A little trace gas carried in dry nitrogen

    If a trace gas is really needed, use only a small quantity with dry nitrogen. A refrigerant and air mixture must not be used because it can be combustible.

    Source: Trane: R-123 Low-Pressure Refrigerant Handling Guidelines (CTV-SVX05H-EN, Aug 2020)

  4. 4.A comfort-cooling chiller in an office tower holds 900 lb of R-123. Under 40 CFR 82.157, above what yearly leak rate must the owner act?

    • A15 percent
    • B20 percent
    • C10 percent
    • D35 percent
    Show the answer

    Answer: C 10 percent

    Comfort cooling appliances, and other appliances with 50 lb or more not in the commercial or industrial groups, have a 10 percent trigger rate.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  5. 5.From January 1, 2026, EPA's AIM Act rule (40 CFR part 84) adds leak repair duties for appliances using HFCs and some substitutes. What is the smallest full charge it covers?

    • A5 lb
    • B50 lb
    • C200 lb
    • D15 lb
    Show the answer

    Answer: D 15 lb

    Section 84.106 applies to appliances with a full charge of 15 lb or more of a regulated substance, or a substitute with a GWP above 53, starting January 1, 2026.

    Source: eCFR: 40 CFR part 84 subpart C, 84.106 Leak repair (2024 AIM Act rule)

  6. 6.The initial verification test on a repaired chiller passed. Within how many days must the follow-up verification test be done?

    • A10 days
    • B30 days
    • C60 days
    • D12 months
    Show the answer

    Answer: A 10 days

    The follow-up verification test is due within 10 days of a successful initial test, or within 10 days of the chiller reaching normal operating conditions if it was evacuated.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  7. 7.A 400-lb R-123 chiller needed 520 lb of refrigerant over one calendar year. What reporting duty does the owner have?

    • ACall EPA within 24 hours of each top-up
    • BSend EPA a report by March 1 of the next year
    • CReport to the local fire department within 30 days
    • DNo report; only repairs are required
    Show the answer

    Answer: B Send EPA a report by March 1 of the next year

    Leaking 130 percent of the charge makes the chiller a chronic leaker. The owner must report to EPA by March 1 of the following year, describing leak-finding and repair efforts.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  8. 8.Carlos runs a standing vacuum decay test on an R-11 chiller and the vacuum is lost. For a required leak inspection, what else must he do?

    • ANothing more; a decay test counts as a full inspection
    • BAdd refrigerant and repeat the decay test in a month
    • CAlso use a method that pinpoints the leak
    • DReport the chiller to EPA as chronically leaking
    Show the answer

    Answer: C Also use a method that pinpoints the leak

    Tests that only show that a system leaks, like pressure or vacuum decay, must be combined with a method that locates the leak.

    Source: eCFR: 40 CFR 82.152 Definitions

Lesson: Low-pressure: leak detection and leak repair

Low-pressure: recovery, recharging and evacuation

Choose your answer first, then open "Show the answer".

  1. 1.To what level must an R-123 chiller be evacuated before opening it for a major repair, using recovery equipment made after November 15, 1993?

    • A0 psig
    • B25 mm Hg absolute
    • C10 inches Hg vacuum
    • D15 inches Hg vacuum
    Show the answer

    Answer: B 25 mm Hg absolute

    The evacuation table sets 25 mm Hg absolute for every low-pressure appliance.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  2. 2.A job will leave a 6-square-inch opening in a chiller's refrigerant circuit uncovered for 40 minutes. How is it classed?

    • AMajor: over 4 sq in open for over 15 minutes
    • BNon-major, because no main component is removed
    • CNon-major, as long as the job ends within an hour
    • DMajor only if the chiller holds over 200 lb
    Show the answer

    Answer: A Major: over 4 sq in open for over 15 minutes

    An opening larger than 4 square inches left uncovered for longer than 15 minutes makes the job major, even if no main component comes out.

    Source: eCFR: 40 CFR 82.152 Definitions

  3. 3.An R-123 chiller must be brought to 0 psig for a non-major repair. R-123 boils below 85°F at standard atmospheric pressure. Which method does the rule forbid?

    • ACirculating controlled hot water through the tubes
    • BUsing the chiller's built-in heating device
    • CWarming the shell with heating blankets
    • DAdding nitrogen, which must later be purged out
    Show the answer

    Answer: D Adding nitrogen, which must later be purged out

    For refrigerants that boil at or below 85°F at 29.9 in Hg, such as R-123 and R-11, methods like nitrogen that need later purging are not allowed. Heat is used instead.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  4. 4.Which methods are allowed to pressurize an R-11 chiller for a non-major repair?

    • ANitrogen, or dry compressed air from the shop
    • BRunning the compressor with the condenser water turned off
    • CControlled hot water or a device such as Prevac
    • DAdding R-22 vapor until it reaches 0 psig
    Show the answer

    Answer: C Controlled hot water or a device such as Prevac

    Controlled hot water and system heating/pressurization devices raise the pressure by warming the refrigerant, without adding any other gas.

    Source: US EPA: Section 608 Technician Certification Test Topics, Type 3 (Low-pressure)

  5. 5.A technician starts recovering refrigerant from a large R-123 chiller. What should be removed first to speed up the job?

    • AThe vapor at the top of the condenser
    • BThe oil in the sump
    • CThe liquid refrigerant
    • DThe air in the purge tank
    Show the answer

    Answer: C The liquid refrigerant

    Recovering liquid at the start moves most of the charge quickly. The vapor is then recovered afterwards.

    Source: US EPA: Section 608 Technician Certification Test Topics, Type 3 (Low-pressure)

  6. 6.All liquid R-123 has been pumped out of a chiller. What is left to do before the chiller can be opened?

    • ANothing; the job is done once all the liquid is out
    • BRecover the leftover vapor to the required vacuum
    • CVent the vapor, since vapor is not regulated
    • DAdd nitrogen to push the vapor out to the room
    Show the answer

    Answer: B Recover the leftover vapor to the required vacuum

    Vapor must be recovered as well as liquid, down to 25 mm Hg absolute. In a big chiller the vapor alone can be many pounds.

    Source: US EPA: Section 608 Technician Certification Test Topics, Type 3 (Low-pressure)

  7. 7.Which of these tasks, by itself, is NOT 'opening an appliance' under the rule?

    • AReplacing the compressor
    • BConnecting hoses to recover refrigerant
    • CCutting a refrigerant line to fit a new valve
    • DRemoving a refrigerant-side flange
    Show the answer

    Answer: B Connecting hoses to recover refrigerant

    Hooking up or removing hoses and gauges, to read pressures, charge or recover, does not count as opening the appliance.

    Source: eCFR: 40 CFR 82.152 Definitions

  8. 8.In a leaky chiller, the condenser section does not leak and can be valved off from the leaking evaporator. What applies to the condenser section?

    • AIt may stay at 0 psig, like the leaking part
    • BIt needs no recovery
    • CIt is pressurized with nitrogen
    • DIsolate it; take it to 25 mm Hg absolute
    Show the answer

    Answer: D Isolate it; take it to 25 mm Hg absolute

    Leaking parts are isolated from non-leaking parts where possible. Non-leaking parts must still reach the normal table level.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  9. 9.Before opening a chiller that has been evacuated, what must the technician do?

    • AAsk the owner to sign a disposal statement form
    • BAdd a small nitrogen holding charge
    • CRun the purge unit for two hours
    • DVerify the required level has been reached
    Show the answer

    Answer: D Verify the required level has been reached

    Before the appliance or part is opened, the technician has to confirm the required vacuum was really reached.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  10. 10.Mei recovers R-123 from one chiller and wants to charge it into another chiller owned by the same university. What does the rule require?

    • AIt must first be reclaimed to the AHRI 700 standard
    • BIt may be reused without recycling or reclaiming
    • CIt must be destroyed
    • DIt must be recycled through a filter-drier twice
    Show the answer

    Answer: B It may be reused without recycling or reclaiming

    Recovered refrigerant may go back into the same appliance or another appliance of the same owner without being recycled or reclaimed.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  11. 11.A low-pressure chiller at 0 psig is open for a small repair, and the section cannot be isolated. What must the technician do with the openings?

    • ALeave them open to let moisture out
    • BBlow nitrogen through them
    • CFill them with oil
    • DCover them
    Show the answer

    Answer: D Cover them

    When isolation is not possible, openings in a pressurized low-pressure appliance must be covered during the repair.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

Lesson: Low-pressure: recovery, recharging and evacuation

Low-pressure: safety and purge units

Choose your answer first, then open "Show the answer".

  1. 1.EPA's Type 3 test topics list equipment-room requirements under ASHRAE Standard 15. For which refrigerants do they name an oxygen-deprivation sensor?

    • AOnly flammable refrigerants
    • BOnly R-123
    • CAll refrigerants
    • DOnly refrigerants with high GWP
    Show the answer

    Answer: C All refrigerants

    EPA's Type 3 topics note that ASHRAE 15 calls for an oxygen-deprivation sensor with all refrigerants. Any large release can push out the air people breathe.

    Source: US EPA: Section 608 Technician Certification Test Topics, Type 3 (Low-pressure)

  2. 2.Where must the alarms from a machinery room refrigerant monitor sound and show, according to a chiller maker's ASHRAE 15 summary?

    • AInside the room and outside each entrance
    • BOnly in the building manager's office upstairs
    • COnly on the chiller's own control panel
    • DOnly at the fire station
    Show the answer

    Answer: A Inside the room and outside each entrance

    The alarms must be both visual and audible, inside the machinery room and outside every entrance.

    Source: Trane: R-123 Low-Pressure Refrigerant Handling Guidelines (CTV-SVX05H-EN, Aug 2020)

  3. 3.How must the required machinery room refrigerant alarms be reset, according to a chiller maker's ASHRAE 15 summary?

    • AAutomatically, once the levels drop back down
    • BFrom any phone, by remote access
    • COnly by a fire department officer
    • DManually, from inside the machinery room
    Show the answer

    Answer: D Manually, from inside the machinery room

    The required alarms are manual-reset types, and the reset is inside the machinery room. Automatic-reset alarms may be added but do not replace them.

    Source: Trane: R-123 Low-Pressure Refrigerant Handling Guidelines (CTV-SVX05H-EN, Aug 2020)

  4. 4.What is the main job of the purge unit on a low-pressure chiller?

    • ATo remove air and moisture from it
    • BTo add refrigerant automatically when low
    • CTo cool the compressor motor
    • DTo relieve pressure above 15 psig
    Show the answer

    Answer: A To remove air and moisture from it

    The purge removes non-condensable gases (mainly air) and water that leak into the low-pressure parts of the chiller.

    Source: Trane: CenTraVac chillers Installation, Operation, and Maintenance (CVHE-SVX005E-EN, 2026)

  5. 5.If air builds up inside a running low-pressure chiller, where does it collect and what does it do?

    • AIn the evaporator, where it freezes the tubes
    • BIn the oil sump, where it thins the oil
    • CIn the purge tank, with no effect on the chiller
    • DIn the condenser, raising head pressure
    Show the answer

    Answer: D In the condenser, raising head pressure

    Non-condensables get trapped in the condenser. They raise condensing pressure and compressor power, and cut efficiency and capacity.

    Source: Trane: CenTraVac chillers Installation, Operation, and Maintenance (CVHE-SVX005E-EN, 2026)

  6. 6.R-11 boils at about 75°F at atmospheric pressure (NIST: 296.9 K). Why does the evaporator of an R-11 chiller run in a vacuum?

    • AThe purge unit pulls a vacuum on it
    • BThe compressor is built to run only in vacuum
    • CTo chill water, it must boil well below 75°F
    • DWater in the tubes pulls the vacuum
    Show the answer

    Answer: C To chill water, it must boil well below 75°F

    To chill water, the refrigerant must boil well below 75°F. Below its atmospheric boiling point, R-11's pressure is below atmospheric, so the evaporator is in a vacuum.

    Source: NIST Chemistry WebBook: trichlorofluoromethane (R-11), phase change data

Lesson: Low-pressure: safety and purge units