What makes a refrigerant low-pressure
EPA calls an appliance low-pressure when its refrigerant has a liquid saturation pressure under 45 psia at 104°F. Examples include R-123 and R-11, plus R-113 and R-245fa.
- NIST gives the normal boiling point of R-11 as 296.9 K (about 75°F) and R-123 as 300.2 K (about 81°F).
- Below those temperatures their pressure is under atmospheric, so a drum of R-123 at 70°F reads a slight vacuum and the evaporator of a running chiller is in a vacuum.
- Pressure rises with temperature. One maker says not to let a shut-down chiller go above 110°F, because rising pressure could burst its 15 psig rupture disc.
The purge unit
- Because parts of the chiller are in a vacuum, air and moisture can leak in.
- Air cannot condense, so it collects in the condenser. There it raises head pressure and power use and lowers capacity.
- The purge unit's job is to remove these non-condensables and water.
- Under ASHRAE 15, the purge exhaust line must meet the same rules as relief-valve piping and be run outdoors.
Machinery room rules under ASHRAE Standard 15
EPA's topic list highlights two points: an oxygen-deprivation sensor with all refrigerants, and a refrigerant sensor in the equipment room for R-123.
- Alarms must be both seen and heard, inside the room and outside each entrance.
- The required alarms reset by hand, from inside the room; automatic-reset alarms may only be extras.
- Mechanical ventilation to the outdoors, which the refrigerant monitor can switch on.
- If the detector shows levels above the exposure limit, ventilate before starting work.
- ASHRAE 15 no longer requires a breathing apparatus (SCBA), but local codes may.
- One maker places the relief vent outlet at least 15 ft above grade and 20 ft from any building opening.
Hazards on the job
- A large release, such as a burst rupture disc, can displace oxygen and cause asphyxiation.
- Refrigerant vapor is heavy and gathers in pits and low areas.
- Do not switch on power to the compressor motor while the chiller is in a deep vacuum; it can damage the motor and compressor.
- To warm a refrigerant cylinder, use only warm water or heat blankets and keep it at or below 150°F. Never use a flame.
Common traps
- Thinking the purge unit is a pressure relief. It removes air and water; overpressure is handled by the rupture disc.
- Believing low toxicity makes a big release safe. Displaced oxygen alone can suffocate people.
- Assuming every machinery room must have an SCBA under ASHRAE 15. The standard dropped that; local codes decide.
- Heating a cylinder with a torch to speed things up. Only warm water or heat blankets, up to 150°F.
Key terms
- ASHRAE Standard 15
- Safety standard for refrigeration systems, including machinery room sensors, alarms and ventilation.
- Oxygen-deprivation sensor
- Monitor that warns when refrigerant has pushed out breathable air; EPA's topic list ties it to all refrigerants.
- Refrigerant sensor (detector)
- Continuous monitor for refrigerant in the room; required for R-123 under ASHRAE 15.
- Non-condensables
- Gases such as air that do not turn to liquid in the condenser and raise head pressure.
- Purge unit
- Device that removes non-condensables and water from a low-pressure chiller.
- Asphyxiation
- Suffocation when refrigerant vapor displaces the oxygen in a room.
- Saturation pressure
- Pressure of a refrigerant with liquid and vapor together at a given temperature; it rises as temperature rises.