Type III safety: machinery rooms, purge units and low-pressure refrigerants

Large low-pressure chillers sit in machinery rooms where a big release can push out breathable air. The Type III test covers ASHRAE Standard 15 room requirements, what the purge unit does, and how low-pressure refrigerants behave with temperature.

What makes a refrigerant low-pressure

EPA calls an appliance low-pressure when its refrigerant has a liquid saturation pressure under 45 psia at 104°F. Examples include R-123 and R-11, plus R-113 and R-245fa.

  • NIST gives the normal boiling point of R-11 as 296.9 K (about 75°F) and R-123 as 300.2 K (about 81°F).
  • Below those temperatures their pressure is under atmospheric, so a drum of R-123 at 70°F reads a slight vacuum and the evaporator of a running chiller is in a vacuum.
  • Pressure rises with temperature. One maker says not to let a shut-down chiller go above 110°F, because rising pressure could burst its 15 psig rupture disc.

The purge unit

  • Because parts of the chiller are in a vacuum, air and moisture can leak in.
  • Air cannot condense, so it collects in the condenser. There it raises head pressure and power use and lowers capacity.
  • The purge unit's job is to remove these non-condensables and water.
  • Under ASHRAE 15, the purge exhaust line must meet the same rules as relief-valve piping and be run outdoors.

Machinery room rules under ASHRAE Standard 15

EPA's topic list highlights two points: an oxygen-deprivation sensor with all refrigerants, and a refrigerant sensor in the equipment room for R-123.

  • Alarms must be both seen and heard, inside the room and outside each entrance.
  • The required alarms reset by hand, from inside the room; automatic-reset alarms may only be extras.
  • Mechanical ventilation to the outdoors, which the refrigerant monitor can switch on.
  • If the detector shows levels above the exposure limit, ventilate before starting work.
  • ASHRAE 15 no longer requires a breathing apparatus (SCBA), but local codes may.
  • One maker places the relief vent outlet at least 15 ft above grade and 20 ft from any building opening.

Hazards on the job

  • A large release, such as a burst rupture disc, can displace oxygen and cause asphyxiation.
  • Refrigerant vapor is heavy and gathers in pits and low areas.
  • Do not switch on power to the compressor motor while the chiller is in a deep vacuum; it can damage the motor and compressor.
  • To warm a refrigerant cylinder, use only warm water or heat blankets and keep it at or below 150°F. Never use a flame.

Common traps

  • Thinking the purge unit is a pressure relief. It removes air and water; overpressure is handled by the rupture disc.
  • Believing low toxicity makes a big release safe. Displaced oxygen alone can suffocate people.
  • Assuming every machinery room must have an SCBA under ASHRAE 15. The standard dropped that; local codes decide.
  • Heating a cylinder with a torch to speed things up. Only warm water or heat blankets, up to 150°F.

Key terms

ASHRAE Standard 15
Safety standard for refrigeration systems, including machinery room sensors, alarms and ventilation.
Oxygen-deprivation sensor
Monitor that warns when refrigerant has pushed out breathable air; EPA's topic list ties it to all refrigerants.
Refrigerant sensor (detector)
Continuous monitor for refrigerant in the room; required for R-123 under ASHRAE 15.
Non-condensables
Gases such as air that do not turn to liquid in the condenser and raise head pressure.
Purge unit
Device that removes non-condensables and water from a low-pressure chiller.
Asphyxiation
Suffocation when refrigerant vapor displaces the oxygen in a room.
Saturation pressure
Pressure of a refrigerant with liquid and vapor together at a given temperature; it rises as temperature rises.

Practise all key terms with flashcards

Try 6 questions on this topic

6 free questions here; 19 on this topic with a pass.

Question 1 of 6

Low-pressure: safety and purge units

EPA's Type 3 test topics list equipment-room requirements under ASHRAE Standard 15. For which refrigerants do they name an oxygen-deprivation sensor?

Low-pressure: safety and purge units: questions with answers

Choose your answer first, then open "Show the answer".

  1. 1.EPA's Type 3 test topics list equipment-room requirements under ASHRAE Standard 15. For which refrigerants do they name an oxygen-deprivation sensor?

    • AOnly flammable refrigerants
    • BOnly R-123
    • CAll refrigerants
    • DOnly refrigerants with high GWP
    Show the answer

    Answer: C All refrigerants

    EPA's Type 3 topics note that ASHRAE 15 calls for an oxygen-deprivation sensor with all refrigerants. Any large release can push out the air people breathe.

    Source: US EPA: Section 608 Technician Certification Test Topics, Type 3 (Low-pressure)

  2. 2.Where must the alarms from a machinery room refrigerant monitor sound and show, according to a chiller maker's ASHRAE 15 summary?

    • AInside the room and outside each entrance
    • BOnly in the building manager's office upstairs
    • COnly on the chiller's own control panel
    • DOnly at the fire station
    Show the answer

    Answer: A Inside the room and outside each entrance

    The alarms must be both visual and audible, inside the machinery room and outside every entrance.

    Source: Trane: R-123 Low-Pressure Refrigerant Handling Guidelines (CTV-SVX05H-EN, Aug 2020)

  3. 3.How must the required machinery room refrigerant alarms be reset, according to a chiller maker's ASHRAE 15 summary?

    • AAutomatically, once the levels drop back down
    • BFrom any phone, by remote access
    • COnly by a fire department officer
    • DManually, from inside the machinery room
    Show the answer

    Answer: D Manually, from inside the machinery room

    The required alarms are manual-reset types, and the reset is inside the machinery room. Automatic-reset alarms may be added but do not replace them.

    Source: Trane: R-123 Low-Pressure Refrigerant Handling Guidelines (CTV-SVX05H-EN, Aug 2020)

  4. 4.What is the main job of the purge unit on a low-pressure chiller?

    • ATo remove air and moisture from it
    • BTo add refrigerant automatically when low
    • CTo cool the compressor motor
    • DTo relieve pressure above 15 psig
    Show the answer

    Answer: A To remove air and moisture from it

    The purge removes non-condensable gases (mainly air) and water that leak into the low-pressure parts of the chiller.

    Source: Trane: CenTraVac chillers Installation, Operation, and Maintenance (CVHE-SVX005E-EN, 2026)

  5. 5.If air builds up inside a running low-pressure chiller, where does it collect and what does it do?

    • AIn the evaporator, where it freezes the tubes
    • BIn the oil sump, where it thins the oil
    • CIn the purge tank, with no effect on the chiller
    • DIn the condenser, raising head pressure
    Show the answer

    Answer: D In the condenser, raising head pressure

    Non-condensables get trapped in the condenser. They raise condensing pressure and compressor power, and cut efficiency and capacity.

    Source: Trane: CenTraVac chillers Installation, Operation, and Maintenance (CVHE-SVX005E-EN, 2026)

  6. 6.R-11 boils at about 75°F at atmospheric pressure (NIST: 296.9 K). Why does the evaporator of an R-11 chiller run in a vacuum?

    • AThe purge unit pulls a vacuum on it
    • BThe compressor is built to run only in vacuum
    • CTo chill water, it must boil well below 75°F
    • DWater in the tubes pulls the vacuum
    Show the answer

    Answer: C To chill water, it must boil well below 75°F

    To chill water, the refrigerant must boil well below 75°F. Below its atmospheric boiling point, R-11's pressure is below atmospheric, so the evaporator is in a vacuum.

    Source: NIST Chemistry WebBook: trichlorofluoromethane (R-11), phase change data