EPA 608 Type II: finding leaks and the leak repair rules

How to spot and test for leaks on high-pressure systems, and what the federal rules require once an appliance leaks too fast: trigger rates, leak rate maths, deadlines and records. The Type II test asks about all of these.

Spotting and testing for leaks

Leak test before you charge or recharge, so new refrigerant does not escape through a leak you missed.

  • Superheat far above normal is a typical leak sign on a high-pressure system.
  • Oil traces on joints or valves often mark the leak, especially on hermetic systems.
  • Test gas order: dry nitrogen alone first, then nitrogen with a trace of R-22 (so an electronic detector can sense it), pure refrigerant last. Never oxygen or compressed air.
  • Sight glass, receiver level, pressure and charging-chart checks only show a loss. Pair them with a method that finds the spot, such as bubbles or an electronic detector.

Which rule and which trigger rate

  • R-22 and other ozone-depleting refrigerants: 40 CFR 82.157 covers appliances of 50 pounds or more.
  • HFCs with a GWP above 53: since 1 January 2026, 40 CFR 84.106 covers appliances of 15 pounds or more, except home and light commercial air conditioners and heat pumps.
  • Trigger rates: commercial refrigeration 20 percent, industrial process refrigeration 30 percent, comfort cooling and everything else 10 percent.
  • Ice rinks count as industrial process refrigeration, and so does any appliance that gives 50 percent or more of its capacity to a process.

Working out the leak rate

The owner calculates the rate each time refrigerant is added, except after a retrofit, a new installation or a seasonal variance, using one method for the whole facility.

  • Annualizing: (pounds added / full charge) / (days since last addition / 365) x 100. Example: 10 lb into a 200 lb system after 73 days = 0.05 / 0.2 = 25 percent.
  • Rolling average: pounds added in the past 365 days / full charge x 100. Example: 30 lb into a 150 lb chiller = 20 percent.

Deadlines and records

  • Repair within 30 days (120 days when the fix needs an industrial process shutdown). A certified technician inspects for the leaks.
  • Initial verification test after the repair, before refrigerant is added back; follow-up test within 10 days.
  • Late parts: up to 30 days after delivery, never past 180 days (270 with a shutdown). The request stands unless EPA objects.
  • Retrofit or retire instead: plan within 30 days, work done within a year of the plan.
  • Keep records three years. Losing at least 125 percent of its full charge within one calendar year means a report to EPA by March 1.

Common traps

  • Using trigger rates from an old study guide: today they are 20 percent for commercial refrigeration, 30 percent for industrial process refrigeration and 10 percent for comfort cooling.
  • Thinking every refrigerant starts at 50 pounds: since 2026, HFC appliances are covered from 15 pounds.
  • Topping off a leaking system: adding refrigerant is not a repair.

Key terms

Leak rate
Percent of the full charge that would be lost in a year at the current rate of loss.
Full charge
The refrigerant amount the appliance needs to run normally.
Trigger rate
The leak rate above which repair is required: 20, 30 or 10 percent.
Industrial process refrigeration
Systems tied to industrial processes, plus ice rinks and industrial ice machines.
Initial verification test
A leak test right after the repair, before refrigerant goes back in.
Follow-up verification test
A second check within 10 days, once the system runs normally.
Seasonal variance
Refrigerant removed for a season and later returned in the same or a smaller amount within 12 months.

Practise all key terms with flashcards

Try 10 questions on this topic

10 free questions here; 32 on this topic with a pass.

Question 1 of 10

High-pressure: leak detection and leak repair

During a walk-through, Dana sees an oily film on a valve and the piping around it on a compressor rack. What should she do next?

High-pressure: leak detection and leak repair: questions with answers

Choose your answer first, then open "Show the answer".

  1. 1.During a walk-through, Dana sees an oily film on a valve and the piping around it on a compressor rack. What should she do next?

    • APinpoint the leak there with bubbles or an electronic detector
    • BWipe the oil off the valve and piping, then close out the call
    • CAdd refrigerant until the sight glass runs clear again
    • DIgnore it, because an oil film is not a refrigerant leak
    Show the answer

    Answer: A Pinpoint the leak there with bubbles or an electronic detector

    Traces of oil are a common sign of a refrigerant leak, especially on hermetic systems. EPA's GreenChill guide says that where oil seepage is seen, a bubble test or electronic detector should be used to find the exact spot.

    Source: US EPA GreenChill: Best Practices Guideline, Commercial Refrigeration Leak Prevention & Repairs (2011)

  2. 2.An electronic leak detector cannot sense pure nitrogen. If some refrigerant is needed for the test, which choice does EPA rank higher than using pure refrigerant?

    • ANitrogen with a trace amount of R-22
    • BA full charge of R-22 with no nitrogen
    • CCompressed air with a trace amount of R-22
    • DOxygen with a trace amount of R-22
    Show the answer

    Answer: A Nitrogen with a trace amount of R-22

    EPA's order is nitrogen alone first, then nitrogen with a trace of HCFC-22, and pure refrigerant last. The trace lets an electronic detector find the leak while using very little refrigerant.

    Source: US EPA: Section 608 Technician Certification Test Topics (Core and Type 2)

  3. 3.Under 40 CFR 82.157, the leak repair rules for ozone-depleting refrigerants such as R-22 apply to appliances with a full charge of at least how much refrigerant?

    • A5 pounds
    • B50 pounds
    • C15 pounds
    • D200 pounds
    Show the answer

    Answer: B 50 pounds

    Since April 10, 2020, 40 CFR 82.157 covers only appliances whose full charge is 50 pounds or more of an ozone-depleting (class I or II) refrigerant, such as R-22.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  4. 4.An office building has an R-22 chiller with 400 pounds of refrigerant. Above what leak rate must it be repaired?

    • A15 percent
    • B10 percent
    • C20 percent
    • D30 percent
    Show the answer

    Answer: B 10 percent

    A chiller that cools occupied space is comfort cooling. 40 CFR 82.157 sets a 10 percent trigger for comfort cooling and other appliances with 50 or more pounds.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  5. 5.A city ice rink uses an R-22 system with 800 pounds of refrigerant. Which trigger leak rate applies?

    • A30 percent, as ice rinks are industrial process refrigeration
    • B10 percent, because the rink is a public building used by people
    • C20 percent, because the rink is a form of cold storage
    • D35 percent, because the system holds more than 500 pounds
    Show the answer

    Answer: A 30 percent, as ice rinks are industrial process refrigeration

    The definition of industrial process refrigeration in 82.152 includes industrial ice machines, power generation cooling and ice rinks, so the 30 percent trigger applies.

    Source: eCFR: 40 CFR 82.152 Definitions

  6. 6.Using the rolling average method: a chiller has a full charge of 150 pounds. Over the past 365 days, 12, 6 and 12 pounds were added. What is the leak rate?

    • A8 percent
    • B20 percent
    • C10 percent
    • D30 percent
    Show the answer

    Answer: B 20 percent

    The rolling average method sums the pounds added over the previous 365 days and divides by the full charge: 30 / 150 = 0.2, or 20 percent.

    Source: eCFR: 40 CFR 82.152 Definitions

  7. 7.An R-22 commercial refrigeration system is found to exceed its trigger rate when refrigerant is added. With no process shutdown needed, how long does the owner have to identify and repair the leaks?

    • A10 days
    • B30 days
    • C120 days
    • DOne year
    Show the answer

    Answer: B 30 days

    Under 82.157(d), leaks must be found and fixed within 30 days of adding refrigerant to an appliance over its trigger rate. Only an industrial process shutdown allows 120 days.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  8. 8.A leaking coil on a large R-22 system was replaced, which meant evacuating that part of the system. When must the initial verification test be done?

    • AAfter the system is recharged and running normally
    • BWithin 10 days after the recharge
    • CBefore any refrigerant is added back
    • DAt the next yearly inspection
    Show the answer

    Answer: C Before any refrigerant is added back

    For repairs that required evacuating the appliance or part of it, the initial verification test must be done before any refrigerant is added.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  9. 9.An owner sends EPA a complete, on-time request for more time to repair leaks under 82.157(f). When is the extension approved?

    • AIt is approved unless EPA tells the owner otherwise
    • BOnly after EPA sends the owner a written approval letter
    • COnly if EPA has not replied within 60 days of receipt
    • DOnly after the state environmental agency signs it
    Show the answer

    Answer: A It is approved unless EPA tells the owner otherwise

    Under 82.157(f), an extension request that meets the conditions is considered approved unless EPA notifies the owner otherwise.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  10. 10.A technician adds R-22 to a customer's 90-pound appliance. What must the technician give the owner when the job ends?

    • ANothing, because only the owner keeps the leak repair records
    • BA service record showing the amount and type of refrigerant added
    • COnly a copy of the technician's Section 608 certification card
    • DNothing to the owner; a leak rate report goes straight to EPA
    Show the answer

    Answer: B A service record showing the amount and type of refrigerant added

    Under 82.157(b), persons adding or removing refrigerant must give the owner documentation at the end of the service, including the amount and type of refrigerant added, so the owner can calculate the leak rate.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair