Which appliances are high-pressure
- High-pressure means a liquid saturation pressure of 170 to 355 psia at 104 °F, as with R-410A, R-22, R-407C or R-502.
- Medium-pressure (45 to 170 psia, e.g. R-134a) and very high-pressure (e.g. R-23) appliances are also Type II work under 40 CFR 82.161; small appliances and vehicle AC are not.
Table 1: how far to evacuate
Levels are in inches of mercury vacuum. They apply to the whole appliance or to an isolated component, so the charge of the part you isolate decides the level. They apply at disposal as well as at service.
- High-pressure, under 200 lb: 0 in Hg, whatever the age of the recovery machine.
- High-pressure, 200 lb or more: 4 in Hg with a machine made before 15 November 1993; 10 in Hg with a newer one.
- Very high-pressure: 0 in Hg.
- You may evacuate just the section being worked on if its refrigerant can be held in a system receiver. Confirm the level before opening.
Exceptions and major repairs
- Non-major repair, with no later evacuation to the air: 0 psig or lower before opening.
- Oil change: 5 psig or lower (or move the oil into a system receiver at that pressure).
- Leaks make Table 1 impossible: non-leaking parts still go to Table 1; leaking parts go as low as you can without fouling the refrigerant, never above 0 psig.
- Major repair: removing the compressor, condenser, evaporator or an auxiliary heat exchange coil, or leaving over 4 square inches of flow area open for over 15 minutes.
- Hooking up gauges or hoses to read pressures, charge or recover is not opening the system.
Recovery techniques and equipment
- Recover liquid first; it is the fastest part.
- Cool the recovery cylinder and warm the appliance. Short, wide hoses also help.
- After reaching the vacuum, wait a few minutes. A pressure rise means refrigerant is still in the system or oil, so keep going.
- Never mix refrigerants; clear the machine, following the maker's steps, before switching refrigerant.
- Passive (system-dependent) recovery is banned above 15 pounds unless it is a permanently attached pump-out unit.
- Machines made after 15 November 1993 need certification by an EPA-approved testing organization.
Where recovered refrigerant may go
- Same appliance or same owner: no recycling or reclaim needed.
- A different owner: reclaim by an EPA-certified reclaimer first.
- Since 1 January 2026, reclaimed refrigerant may hold at most 15 percent virgin HFC by weight.
Common traps
- Looking at the whole system's charge when only a part is isolated: the isolated part's charge sets the Table 1 level.
- Using the 0 psig shortcut at disposal: it is only for non-major repairs, so disposal needs the full Table 1 level.
- Thinking recycled refrigerant can be sold to another customer: a change of owner needs reclaim.
Key terms
- High-pressure appliance
- Uses a refrigerant with a liquid saturation pressure of 170 to 355 psia at 104 °F, such as R-410A or R-22.
- Table 1
- The chart in 40 CFR 82.156 that sets the vacuum level to reach before opening or disposing of an appliance.
- Major repair
- Removing the compressor, condenser, evaporator or an auxiliary coil, or leaving more than 4 sq in open for over 15 minutes.
- System receiver
- The isolated part or vessel of an appliance that holds the charge while another part is serviced.
- System-dependent recovery
- Recovery that relies on the appliance's own parts, such as its compressor; limited to systems of 15 pounds or less.
- Recycle
- Clean refrigerant, for example with filter-driers, for reuse by the same owner.
- Reclaim
- Reprocess refrigerant to the AHRI 700 purity standard and verify it; needed before it changes owner.