Type II (high-pressure)

EPA 608 Type II: required evacuation levels and recovery techniques

Before opening or scrapping a high-pressure appliance, you must recover its refrigerant to a set vacuum level. This lesson covers Table 1, the exceptions, major repairs, faster recovery and where recovered refrigerant may go.

Which appliances are high-pressure

  • High-pressure means a liquid saturation pressure of 170 to 355 psia at 104 °F, as with R-410A, R-22, R-407C or R-502.
  • Medium-pressure (45 to 170 psia, e.g. R-134a) and very high-pressure (e.g. R-23) appliances are also Type II work under 40 CFR 82.161; small appliances and vehicle AC are not.

Table 1: how far to evacuate

Levels are in inches of mercury vacuum. They apply to the whole appliance or to an isolated component, so the charge of the part you isolate decides the level. They apply at disposal as well as at service.

  • High-pressure, under 200 lb: 0 in Hg, whatever the age of the recovery machine.
  • High-pressure, 200 lb or more: 4 in Hg with a machine made before 15 November 1993; 10 in Hg with a newer one.
  • Very high-pressure: 0 in Hg.
  • You may evacuate just the section being worked on if its refrigerant can be held in a system receiver. Confirm the level before opening.

Exceptions and major repairs

  • Non-major repair, with no later evacuation to the air: 0 psig or lower before opening.
  • Oil change: 5 psig or lower (or move the oil into a system receiver at that pressure).
  • Leaks make Table 1 impossible: non-leaking parts still go to Table 1; leaking parts go as low as you can without fouling the refrigerant, never above 0 psig.
  • Major repair: removing the compressor, condenser, evaporator or an auxiliary heat exchange coil, or leaving over 4 square inches of flow area open for over 15 minutes.
  • Hooking up gauges or hoses to read pressures, charge or recover is not opening the system.

Recovery techniques and equipment

  • Recover liquid first; it is the fastest part.
  • Cool the recovery cylinder and warm the appliance. Short, wide hoses also help.
  • After reaching the vacuum, wait a few minutes. A pressure rise means refrigerant is still in the system or oil, so keep going.
  • Never mix refrigerants; clear the machine, following the maker's steps, before switching refrigerant.
  • Passive (system-dependent) recovery is banned above 15 pounds unless it is a permanently attached pump-out unit.
  • Machines made after 15 November 1993 need certification by an EPA-approved testing organization.

Where recovered refrigerant may go

  • Same appliance or same owner: no recycling or reclaim needed.
  • A different owner: reclaim by an EPA-certified reclaimer first.
  • Since 1 January 2026, reclaimed refrigerant may hold at most 15 percent virgin HFC by weight.

Common traps

  • Looking at the whole system's charge when only a part is isolated: the isolated part's charge sets the Table 1 level.
  • Using the 0 psig shortcut at disposal: it is only for non-major repairs, so disposal needs the full Table 1 level.
  • Thinking recycled refrigerant can be sold to another customer: a change of owner needs reclaim.

Key terms

High-pressure appliance
Uses a refrigerant with a liquid saturation pressure of 170 to 355 psia at 104 °F, such as R-410A or R-22.
Table 1
The chart in 40 CFR 82.156 that sets the vacuum level to reach before opening or disposing of an appliance.
Major repair
Removing the compressor, condenser, evaporator or an auxiliary coil, or leaving more than 4 sq in open for over 15 minutes.
System receiver
The isolated part or vessel of an appliance that holds the charge while another part is serviced.
System-dependent recovery
Recovery that relies on the appliance's own parts, such as its compressor; limited to systems of 15 pounds or less.
Recycle
Clean refrigerant, for example with filter-driers, for reuse by the same owner.
Reclaim
Reprocess refrigerant to the AHRI 700 purity standard and verify it; needed before it changes owner.

Practise all key terms with flashcards

Try 10 questions on this topic

10 free questions here; 32 on this topic with a pass.

Question 1 of 10

High-pressure: recovery requirements and techniques

How do EPA's rules define a high-pressure appliance?

High-pressure: recovery requirements and techniques: questions with answers

Choose your answer first, then open "Show the answer".

  1. 1.How do EPA's rules define a high-pressure appliance?

    • AIts refrigerant's liquid saturation pressure is under 45 psia at 104 °F
    • BIts refrigerant's liquid saturation pressure is 45 to 170 psia at 104 °F
    • CIts refrigerant's liquid saturation pressure is 170 to 355 psia at 104 °F
    • DIts refrigerant has a critical temperature below 104 °F
    Show the answer

    Answer: C Its refrigerant's liquid saturation pressure is 170 to 355 psia at 104 °F

    40 CFR 82.152 classes an appliance as high-pressure when, at 104 °F, its refrigerant's liquid saturation pressure is from 170 to 355 psia.

    Source: eCFR: 40 CFR 82.152 Definitions

  2. 2.Under 40 CFR 82.161, which certification covers a technician who services an R-134a chiller, a medium-pressure appliance?

    • AType II
    • BType I
    • CType III
    • DNo certification, since R-134a is not ozone-depleting
    Show the answer

    Answer: A Type II

    40 CFR 82.161 puts medium-pressure appliances in Type II, together with high- and very high-pressure ones (small appliances and vehicle AC are excluded).

    Source: eCFR: 40 CFR 82.161 Technician certification

  3. 3.An R-22 chiller holds 350 pounds. Using recovery equipment made in 2018, to what level must it be evacuated before a major repair?

    • A10 inches of mercury vacuum
    • B0 inches of mercury vacuum
    • C4 inches of mercury vacuum
    • D25 mm of mercury absolute
    Show the answer

    Answer: A 10 inches of mercury vacuum

    Table 1 sets 10 inches of mercury vacuum for high-pressure appliances with 200 pounds or more when using equipment made on or after 15 November 1993.

    Source: US EPA: Stationary Refrigeration Service Practice Requirements

  4. 4.Must a technician always evacuate the whole appliance before opening it?

    • ANo, only the part being serviced, if isolated to a system receiver
    • BYes, the whole appliance must always be evacuated, every time
    • CNo, the technician may close the service valves and open the part
    • DYes, unless the system holds less than 200 pounds of refrigerant
    Show the answer

    Answer: A No, only the part being serviced, if isolated to a system receiver

    82.156(a) allows evacuating just the section being worked on, as long as its refrigerant can be held in a system receiver.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  5. 5.A 250-pound R-22 chiller with no leaks is being scrapped, using a recovery machine made in 2020. Can the technician stop at 0 psig, as for a non-major repair?

    • AYes; 0 psig is enough for any job on a high-pressure system
    • BYes; disposal needs no set level once the unit is shut down
    • CNo; it must reach the Table 1 level of 10 inches Hg
    • DNo; disposal needs a deep vacuum of 500 microns or lower
    Show the answer

    Answer: C No; it must reach the Table 1 level of 10 inches Hg

    82.156(a) requires technicians to evacuate refrigerant, including all liquid, to the Table 1 levels before opening or disposing of these appliances. For 200 pounds or more with post-1993 equipment, that is 10 inches Hg.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  6. 6.A rooftop unit holds 25 pounds of R-22. May the technician use system-dependent (passive) recovery equipment on it?

    • AYes, if the compressor is working
    • BNo, unless it is a permanently attached pump-out unit
    • CYes, for any high-pressure appliance
    • DNo, because system-dependent equipment is allowed only on low-pressure chillers
    Show the answer

    Answer: B No, unless it is a permanently attached pump-out unit

    82.156(e) says system-dependent equipment may not be used on appliances with more than 15 pounds of refrigerant, unless it is permanently attached as a pump-out unit.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  7. 7.Before changing the compressor oil in an R-22 system, how low must the pressure be?

    • ANo higher than 0 psig
    • B10 inches of mercury vacuum
    • CNo higher than 15 psig
    • DNo higher than 5 psig
    Show the answer

    Answer: D No higher than 5 psig

    EPA treats an oil change above 5 psig as a violation, because the oil holds dissolved refrigerant. The oil may also be drained into a system receiver brought to 5 psig or less.

    Source: US EPA: Stationary Refrigeration Service Practice Requirements

  8. 8.Which hose setup gives the fastest recovery?

    • AShort hoses with a large inside diameter
    • BLong hoses with a small inside diameter
    • CLong hoses with a large inside diameter
    • DShort hoses with a small inside diameter
    Show the answer

    Answer: A Short hoses with a large inside diameter

    EPA lists hose length and diameter among the factors that affect recovery speed. Shorter, wider hoses give less restriction and faster recovery.

    Source: US EPA: Section 608 Technician Certification Test Topics (Core and Type 2)

  9. 9.Mia's recovery machine was last used on R-22. She now needs it for R-410A. What should she do first?

    • ANothing, because small amounts of R-22 left inside do not matter
    • BClear the R-22 out of the machine using the maker's steps
    • CRecover the R-410A into the same cylinder as the R-22
    • DRelease the R-22 left in the machine to the outside air
    Show the answer

    Answer: B Clear the R-22 out of the machine using the maker's steps

    EPA's topics cover the need to avoid mixing refrigerants and to reduce cross-contamination when a recovery machine is used with a new refrigerant. Recovery equipment must be used according to the manufacturer's directions.

    Source: US EPA: Section 608 Technician Certification Test Topics (Core and Type 2)

  10. 10.A technician recovers refrigerant to dispose of a 30-pound R-22 rooftop unit. For how long must the disposal records be kept?

    • AOne year
    • BThree years
    • CFive years
    • DNo records are needed under 50 pounds
    Show the answer

    Answer: B Three years

    When disposing of appliances that hold over 5 but under 50 pounds, technicians keep records of the company, location, date and refrigerant type for three years.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances