Protecting yourself
- Refrigerants can bring toxicity, flammability, asphyxiation and physical hazards (EPA refrigerant safety page).
- Exposure risks include oxygen deprivation, heart (cardiac) effects, frostbite and long-term harm. A big leak in a closed room can push out the air you breathe.
- Wear gloves and goggles. In extreme cases, such as a room where the oxygen may be low, use a self-contained breathing apparatus (SCBA).
- EPA's Type II topics list an oxygen deprivation sensor for equipment rooms under ASHRAE Standard 15, whatever refrigerant is used.
- Never energize a hermetic compressor while the system is under a vacuum; the motor can be damaged.
Nitrogen, pressure and relief valves
- Pressurize with nitrogen, never oxygen or compressed air, and always through a pressure regulator with a relief valve.
- A pressure relief valve should not discharge in normal running. EPA's GreenChill guide says that if one has, find and fix the cause and replace the valve, which is built for one release and may seep later.
- To use a chart in absolute pressure, add 14.7 to the gauge reading: 100 psig is 114.7 psia.
Cylinders
- Recover only into reusable recovery cylinders that are DOT-approved; they are gray with a yellow top.
- Never refill a disposable cylinder.
- Fill a cylinder no more than 80 percent, because liquid expands as it warms.
- From 1 January 2028, a used disposable cylinder holding an HFC that you will not use again must go for heel removal, for example to a certified reclaimer or a refrigerant supplier that can do it. A certified technician may instead evacuate the heel to 15 in Hg and give the scrap yard a signed statement.
Charging and retrofits
- Leak test before charging or recharging.
- Do not add extra refrigerant as a buffer. GreenChill notes that the extra charge only adds to what a leak can release.
- Hydrocarbons such as propane are not approved for retrofitting high-pressure equipment.
- From 1 January 2029, HFC equipment in supermarkets, automatic commercial ice makers and refrigerated transport must be serviced with reclaimed refrigerant that meets the 15 percent virgin limit.
Disposal
- Equipment that is usually taken apart on site, such as central home air conditioning, chillers and retail food refrigeration, must have its refrigerant recovered under the servicing rules before disposal. The Table 1 levels apply.
- The scrap-yard signed-statement route is for appliances that reach the waste stream with their charge intact, like household fridges and window units. EPA does not accept a sticker as proof.
- Releasing refrigerant on purpose after you have recovered it, even if it is dirty, is venting and breaks the law. Send it for reclaim instead.
- For appliances over 5 and under 50 pounds that you dispose of, keep recovery records for three years.
Common traps
- Filling a recovery cylinder to 90 or 100 percent: stop at 80 percent.
- Using compressed air or oxygen to pressurize a system: use nitrogen with a regulator and relief valve.
- Running the compressor to help an evacuation: never energize a hermetic compressor under vacuum.
- Venting refrigerant because it is contaminated: recovered refrigerant still may not be released.
Key terms
- SCBA
- Self-contained breathing apparatus: a breathing set with its own air supply, for extreme cases such as low oxygen.
- Oxygen deprivation
- Not enough oxygen to breathe, which can happen when leaking refrigerant displaces air in a closed room.
- ASHRAE Standard 15
- The safety standard for refrigeration systems that sets equipment room requirements, such as sensors.
- Recovery cylinder
- A reusable, DOT-approved cylinder, gray with a yellow top, for holding recovered refrigerant.
- Disposable cylinder
- A one-trip cylinder for new refrigerant; it must never be refilled.
- Heel
- The refrigerant left in a cylinder after normal use.
- psia
- Pounds per square inch absolute: the gauge reading (psig) plus 14.7.