Why low-pressure leaks look different
In an R-123 or R-11 chiller, parts of the machine sit below atmospheric pressure, running or not. A leak there lets air and moisture in.
- The purge unit removes that air, so a purge that runs far more than normal is the classic leak sign.
- One maker judges leak size from daily purge minutes; a 'large leak' reading calls for an immediate leak check.
- Suspect a leak? Leak-test before adding refrigerant.
Pressurizing for a leak test
- First choice: warm the refrigerant with controlled hot water or a built-in heating device such as Prevac. Heat adds no gas that must be removed later.
- Second choice: dry nitrogen.
- Keep test pressure low: on many chillers the evaporator rupture disc bursts at about 15 psig. One maker's R-123 guide tests with nitrogen at 8 psig and soap solution.
- If a trace gas is truly needed, use a small amount carried in dry nitrogen. Never use a refrigerant and air mix, which could burn.
Leak repair rules (40 CFR 82.157)
Since April 10, 2020, these rules cover appliances with 50 lb or more of a class I or II (ozone-depleting) refrigerant. The owner calculates the leak rate at each refrigerant addition, with a few exceptions.
- Trigger rates over 12 months: 10% for comfort cooling (most chillers), 20% for commercial refrigeration, 30% for industrial process refrigeration.
- Over the trigger, the owner has 30 days to find and fix leaks (120 when a process shutdown is needed).
- A certified technician finds the leaks. An initial verification test follows the repair (before recharging if the system was evacuated), and a follow-up test comes within 10 days.
- Late parts: up to 30 days after delivery, capped at 180 days (270 with a process shutdown).
- Choosing to retrofit or retire instead? The plan is due within 30 days and the work within one year.
Inspections, chronic leakers and the 2026 HFC rule
- After exceeding the rate, comfort-cooling chillers get a yearly leak inspection; commercial and industrial systems of 500 lb or more get one every three months.
- A decay test only shows that a leak exists. Pair it with a method that finds where it is, such as an electronic detector or bubbles.
- Losing 125% or more of the full charge within one calendar year means a report to EPA by March 1.
- Purged refrigerant is left out of the leak rate only if it is destroyed at a verified 98% or better.
- From January 1, 2026, 40 CFR part 84 adds similar duties for HFC appliances (and substitutes with GWP over 53) holding 15 lb or more.
Common traps
- Thinking nitrogen is the first choice for a low-pressure leak test. Heat (hot water or a device like Prevac) comes first; nitrogen is second.
- Using the old 15% and 35% leak rates. Since 2019 the rates are 10% (comfort cooling), 20% (commercial) and 30% (industrial process).
- Treating a pressure-decay test as a full leak inspection. It must be paired with a method that locates the leak.
Key terms
- Low-pressure appliance
- Uses a refrigerant whose liquid saturation pressure is under 45 psia at 104°F, such as R-11 or R-123.
- Purge unit
- Device on a low-pressure chiller that removes air and water; heavy purge running points to a leak.
- Rupture disc
- Safety disc on the evaporator that protects the shell; on many chillers it bursts at about 15 psig.
- Trigger leak rate
- Yearly leak rate above which repairs are required: 10%, 20% or 30% depending on the appliance type.
- Initial verification test
- Leak test right after a repair, before refrigerant goes back in when the system was evacuated.
- Follow-up verification test
- Second check within 10 days, once the chiller runs normally, that the repair held.
- Chronically leaking appliance
- One that loses 125% or more of its full charge in a calendar year; it must be reported to EPA.