Type III leak testing and leak repair for low-pressure chillers

Low-pressure chillers (R-11, R-123 and similar) run partly in a vacuum, so leaks pull air in instead of pushing refrigerant out. The Type III test asks how to pressurize these chillers for a leak test, how to spot a leak, and what the EPA leak repair rules require of owners.

Why low-pressure leaks look different

In an R-123 or R-11 chiller, parts of the machine sit below atmospheric pressure, running or not. A leak there lets air and moisture in.

  • The purge unit removes that air, so a purge that runs far more than normal is the classic leak sign.
  • One maker judges leak size from daily purge minutes; a 'large leak' reading calls for an immediate leak check.
  • Suspect a leak? Leak-test before adding refrigerant.

Pressurizing for a leak test

  • First choice: warm the refrigerant with controlled hot water or a built-in heating device such as Prevac. Heat adds no gas that must be removed later.
  • Second choice: dry nitrogen.
  • Keep test pressure low: on many chillers the evaporator rupture disc bursts at about 15 psig. One maker's R-123 guide tests with nitrogen at 8 psig and soap solution.
  • If a trace gas is truly needed, use a small amount carried in dry nitrogen. Never use a refrigerant and air mix, which could burn.

Leak repair rules (40 CFR 82.157)

Since April 10, 2020, these rules cover appliances with 50 lb or more of a class I or II (ozone-depleting) refrigerant. The owner calculates the leak rate at each refrigerant addition, with a few exceptions.

  • Trigger rates over 12 months: 10% for comfort cooling (most chillers), 20% for commercial refrigeration, 30% for industrial process refrigeration.
  • Over the trigger, the owner has 30 days to find and fix leaks (120 when a process shutdown is needed).
  • A certified technician finds the leaks. An initial verification test follows the repair (before recharging if the system was evacuated), and a follow-up test comes within 10 days.
  • Late parts: up to 30 days after delivery, capped at 180 days (270 with a process shutdown).
  • Choosing to retrofit or retire instead? The plan is due within 30 days and the work within one year.

Inspections, chronic leakers and the 2026 HFC rule

  • After exceeding the rate, comfort-cooling chillers get a yearly leak inspection; commercial and industrial systems of 500 lb or more get one every three months.
  • A decay test only shows that a leak exists. Pair it with a method that finds where it is, such as an electronic detector or bubbles.
  • Losing 125% or more of the full charge within one calendar year means a report to EPA by March 1.
  • Purged refrigerant is left out of the leak rate only if it is destroyed at a verified 98% or better.
  • From January 1, 2026, 40 CFR part 84 adds similar duties for HFC appliances (and substitutes with GWP over 53) holding 15 lb or more.

Common traps

  • Thinking nitrogen is the first choice for a low-pressure leak test. Heat (hot water or a device like Prevac) comes first; nitrogen is second.
  • Using the old 15% and 35% leak rates. Since 2019 the rates are 10% (comfort cooling), 20% (commercial) and 30% (industrial process).
  • Treating a pressure-decay test as a full leak inspection. It must be paired with a method that locates the leak.

Key terms

Low-pressure appliance
Uses a refrigerant whose liquid saturation pressure is under 45 psia at 104°F, such as R-11 or R-123.
Purge unit
Device on a low-pressure chiller that removes air and water; heavy purge running points to a leak.
Rupture disc
Safety disc on the evaporator that protects the shell; on many chillers it bursts at about 15 psig.
Trigger leak rate
Yearly leak rate above which repairs are required: 10%, 20% or 30% depending on the appliance type.
Initial verification test
Leak test right after a repair, before refrigerant goes back in when the system was evacuated.
Follow-up verification test
Second check within 10 days, once the chiller runs normally, that the repair held.
Chronically leaking appliance
One that loses 125% or more of its full charge in a calendar year; it must be reported to EPA.

Practise all key terms with flashcards

Try 8 questions on this topic

8 free questions here; 26 on this topic with a pass.

Question 1 of 8

Low-pressure: leak detection and leak repair

A technician must raise the pressure inside an R-123 chiller to look for leaks. Which method comes first in the usual order of preference?

Low-pressure: leak detection and leak repair: questions with answers

Choose your answer first, then open "Show the answer".

  1. 1.A technician must raise the pressure inside an R-123 chiller to look for leaks. Which method comes first in the usual order of preference?

    • AHot water or a built-in heater such as Prevac
    • BDry nitrogen from a cylinder with a regulator and relief valve
    • CCompressed shop air, dried through a filter
    • DRefrigerant vapor mixed with air
    Show the answer

    Answer: A Hot water or a built-in heater such as Prevac

    For low-pressure systems the first choice is to warm the refrigerant: hot water through the tubes or a built-in heating/pressurization device. Heat raises the pressure without adding a gas that later has to be purged.

    Source: US EPA: Section 608 Technician Certification Test Topics, Type 3 (Low-pressure)

  2. 2.Why does a leak in a running R-123 chiller often let air in instead of letting refrigerant out?

    • AR-123 vapor is heavier than air, so it stays inside
    • BParts of it are below atmospheric pressure
    • CThe rupture disc holds refrigerant in and lets air pass
    • DThe purge unit seals small holes as it runs
    Show the answer

    Answer: B Parts of it are below atmospheric pressure

    Low-pressure refrigerants let sections of the chiller sit below atmospheric pressure, running or not. Where inside pressure is lower, a leak draws air and moisture in.

    Source: Trane: CenTraVac chillers Installation, Operation, and Maintenance (CVHE-SVX005E-EN, 2026)

  3. 3.A leak on an R-123 chiller is too small to find with nitrogen and soap. What does the maker's guide say to use?

    • AA mixture of refrigerant and air, which shows up well
    • BPure refrigerant vapor raised to 15 psig
    • COxygen, so the leak shows up faster
    • DA little trace gas carried in dry nitrogen
    Show the answer

    Answer: D A little trace gas carried in dry nitrogen

    If a trace gas is really needed, use only a small quantity with dry nitrogen. A refrigerant and air mixture must not be used because it can be combustible.

    Source: Trane: R-123 Low-Pressure Refrigerant Handling Guidelines (CTV-SVX05H-EN, Aug 2020)

  4. 4.A comfort-cooling chiller in an office tower holds 900 lb of R-123. Under 40 CFR 82.157, above what yearly leak rate must the owner act?

    • A15 percent
    • B20 percent
    • C10 percent
    • D35 percent
    Show the answer

    Answer: C 10 percent

    Comfort cooling appliances, and other appliances with 50 lb or more not in the commercial or industrial groups, have a 10 percent trigger rate.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  5. 5.From January 1, 2026, EPA's AIM Act rule (40 CFR part 84) adds leak repair duties for appliances using HFCs and some substitutes. What is the smallest full charge it covers?

    • A5 lb
    • B50 lb
    • C200 lb
    • D15 lb
    Show the answer

    Answer: D 15 lb

    Section 84.106 applies to appliances with a full charge of 15 lb or more of a regulated substance, or a substitute with a GWP above 53, starting January 1, 2026.

    Source: eCFR: 40 CFR part 84 subpart C, 84.106 Leak repair (2024 AIM Act rule)

  6. 6.The initial verification test on a repaired chiller passed. Within how many days must the follow-up verification test be done?

    • A10 days
    • B30 days
    • C60 days
    • D12 months
    Show the answer

    Answer: A 10 days

    The follow-up verification test is due within 10 days of a successful initial test, or within 10 days of the chiller reaching normal operating conditions if it was evacuated.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  7. 7.A 400-lb R-123 chiller needed 520 lb of refrigerant over one calendar year. What reporting duty does the owner have?

    • ACall EPA within 24 hours of each top-up
    • BSend EPA a report by March 1 of the next year
    • CReport to the local fire department within 30 days
    • DNo report; only repairs are required
    Show the answer

    Answer: B Send EPA a report by March 1 of the next year

    Leaking 130 percent of the charge makes the chiller a chronic leaker. The owner must report to EPA by March 1 of the following year, describing leak-finding and repair efforts.

    Source: eCFR: 40 CFR 82.157 Appliance maintenance and leak repair

  8. 8.Carlos runs a standing vacuum decay test on an R-11 chiller and the vacuum is lost. For a required leak inspection, what else must he do?

    • ANothing more; a decay test counts as a full inspection
    • BAdd refrigerant and repeat the decay test in a month
    • CAlso use a method that pinpoints the leak
    • DReport the chiller to EPA as chronically leaking
    Show the answer

    Answer: C Also use a method that pinpoints the leak

    Tests that only show that a system leaks, like pressure or vacuum decay, must be combined with a method that locates the leak.

    Source: eCFR: 40 CFR 82.152 Definitions