Type III recovery, evacuation and recharging of low-pressure chillers

Before a low-pressure chiller is opened or scrapped, its refrigerant must be recovered to a deep vacuum, with a few exceptions for small repairs and leaks. The Type III test checks the required levels, the pressurizing rules for non-major repairs, and the practical steps that keep water tubes from freezing.

How deep to evacuate

Every low-pressure appliance must reach 25 mm Hg absolute before it is opened for a major repair or disposed of. That is roughly 29 inches of mercury vacuum.

  • The level is the same with recovery equipment made before or after November 15, 1993.
  • Charge size does not change it: the 200-lb split only matters for high- and medium-pressure units.
  • Recover all the refrigerant, liquid and vapor, and confirm the level is reached before opening.
  • You may evacuate just the part being serviced if its refrigerant can be held in a system receiver.

Major and non-major repairs

A repair is major if it removes the compressor, condenser, evaporator or an auxiliary heat exchange coil, or leaves more than 4 square inches open for more than 15 minutes.

  • Non-major repair, not followed by evacuating the chiller to the atmosphere: bring the chiller up to no more than 0 psig before opening, and cover openings if the section cannot be isolated.
  • For refrigerants that boil at or below 85°F at atmospheric pressure (R-11, R-123), use heat only: controlled hot water or a device such as Prevac. Nitrogen is not allowed because it would have to be purged out later.
  • For refrigerants that boil above 85°F (R-113), heat as far as you can, then nitrogen may finish the job up to atmospheric.
  • Oil changes: no higher than 5 psig. Warming the oil to about 130°F first drives out dissolved refrigerant.
  • Leaky chiller that cannot reach 25 mm Hg absolute without contaminating the refrigerant: isolate the leak, take non-leaking parts to the full level, and leaking parts as low as practical, never above 0 psig.

Recovery and recharging technique

  • Take the liquid out first, then recover the vapor.
  • Keep water circulating through the tubes, or drain them, while the refrigerant is pulled out. Falling pressure chills the refrigerant enough to freeze still water.
  • After reaching the vacuum, wait a few minutes. A pressure rise means refrigerant is still boiling off from liquid or oil.
  • When recharging, put vapor in first, then liquid, so the tubes do not freeze.
  • Charge centrifugal chillers through the evaporator charging valve.

Equipment and refrigerant reuse

  • Machines made from November 15, 1993 need certification by an EPA-approved testing organization; older ones count as certified if they reach the required level on a calibrated gauge.
  • Follow the maker's directions unless they conflict with the federal rules.
  • System-dependent equipment is not allowed on charges over 15 lb unless it is a permanently attached pump-out unit.
  • Refrigerant can go back into the same owner's chillers without reclaiming; a new owner means it must be reclaimed first.

Common traps

  • Assuming old recovery machines get an easier level. For low-pressure appliances it is 25 mm Hg absolute either way.
  • Using nitrogen to reach 0 psig on an R-123 chiller. R-123 boils below 85°F, so only heat methods are allowed.
  • Charging liquid into a chiller in deep vacuum. Start with vapor or the water in the tubes can freeze.
  • Stopping once the liquid is out. The vapor must be recovered too, and a rising pressure after reaching the vacuum means the job is not done.

Key terms

25 mm Hg absolute
Required recovery level for every low-pressure appliance, about 29 inches of mercury vacuum.
Major repair
Removes the compressor, condenser, evaporator or auxiliary coil, or leaves over 4 sq in open for over 15 minutes.
0 psig
Atmospheric pressure; the highest pressure allowed when opening a low-pressure chiller for a non-major repair.
Controlled hot water
Warm water run through the tubes to raise refrigerant pressure without adding gas.
Evaporator charging valve
The usual point for charging refrigerant into a centrifugal chiller.
Pump-out unit
Recovery equipment permanently attached to a chiller; the only system-dependent equipment allowed over 15 lb.
Reclaim
Reprocess refrigerant to the AHRI 700 purity standard; needed when recovered refrigerant changes owner.

Practise all key terms with flashcards

Try 10 questions on this topic

11 free questions here; 35 on this topic with a pass.

Question 1 of 10

Low-pressure: recovery, recharging and evacuation

To what level must an R-123 chiller be evacuated before opening it for a major repair, using recovery equipment made after November 15, 1993?

Low-pressure: recovery, recharging and evacuation: questions with answers

Choose your answer first, then open "Show the answer".

  1. 1.To what level must an R-123 chiller be evacuated before opening it for a major repair, using recovery equipment made after November 15, 1993?

    • A0 psig
    • B25 mm Hg absolute
    • C10 inches Hg vacuum
    • D15 inches Hg vacuum
    Show the answer

    Answer: B 25 mm Hg absolute

    The evacuation table sets 25 mm Hg absolute for every low-pressure appliance.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  2. 2.A job will leave a 6-square-inch opening in a chiller's refrigerant circuit uncovered for 40 minutes. How is it classed?

    • AMajor: over 4 sq in open for over 15 minutes
    • BNon-major, because no main component is removed
    • CNon-major, as long as the job ends within an hour
    • DMajor only if the chiller holds over 200 lb
    Show the answer

    Answer: A Major: over 4 sq in open for over 15 minutes

    An opening larger than 4 square inches left uncovered for longer than 15 minutes makes the job major, even if no main component comes out.

    Source: eCFR: 40 CFR 82.152 Definitions

  3. 3.An R-123 chiller must be brought to 0 psig for a non-major repair. R-123 boils below 85°F at standard atmospheric pressure. Which method does the rule forbid?

    • ACirculating controlled hot water through the tubes
    • BUsing the chiller's built-in heating device
    • CWarming the shell with heating blankets
    • DAdding nitrogen, which must later be purged out
    Show the answer

    Answer: D Adding nitrogen, which must later be purged out

    For refrigerants that boil at or below 85°F at 29.9 in Hg, such as R-123 and R-11, methods like nitrogen that need later purging are not allowed. Heat is used instead.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  4. 4.Which methods are allowed to pressurize an R-11 chiller for a non-major repair?

    • ANitrogen, or dry compressed air from the shop
    • BRunning the compressor with the condenser water turned off
    • CControlled hot water or a device such as Prevac
    • DAdding R-22 vapor until it reaches 0 psig
    Show the answer

    Answer: C Controlled hot water or a device such as Prevac

    Controlled hot water and system heating/pressurization devices raise the pressure by warming the refrigerant, without adding any other gas.

    Source: US EPA: Section 608 Technician Certification Test Topics, Type 3 (Low-pressure)

  5. 5.A technician starts recovering refrigerant from a large R-123 chiller. What should be removed first to speed up the job?

    • AThe vapor at the top of the condenser
    • BThe oil in the sump
    • CThe liquid refrigerant
    • DThe air in the purge tank
    Show the answer

    Answer: C The liquid refrigerant

    Recovering liquid at the start moves most of the charge quickly. The vapor is then recovered afterwards.

    Source: US EPA: Section 608 Technician Certification Test Topics, Type 3 (Low-pressure)

  6. 6.All liquid R-123 has been pumped out of a chiller. What is left to do before the chiller can be opened?

    • ANothing; the job is done once all the liquid is out
    • BRecover the leftover vapor to the required vacuum
    • CVent the vapor, since vapor is not regulated
    • DAdd nitrogen to push the vapor out to the room
    Show the answer

    Answer: B Recover the leftover vapor to the required vacuum

    Vapor must be recovered as well as liquid, down to 25 mm Hg absolute. In a big chiller the vapor alone can be many pounds.

    Source: US EPA: Section 608 Technician Certification Test Topics, Type 3 (Low-pressure)

  7. 7.Which of these tasks, by itself, is NOT 'opening an appliance' under the rule?

    • AReplacing the compressor
    • BConnecting hoses to recover refrigerant
    • CCutting a refrigerant line to fit a new valve
    • DRemoving a refrigerant-side flange
    Show the answer

    Answer: B Connecting hoses to recover refrigerant

    Hooking up or removing hoses and gauges, to read pressures, charge or recover, does not count as opening the appliance.

    Source: eCFR: 40 CFR 82.152 Definitions

  8. 8.In a leaky chiller, the condenser section does not leak and can be valved off from the leaking evaporator. What applies to the condenser section?

    • AIt may stay at 0 psig, like the leaking part
    • BIt needs no recovery
    • CIt is pressurized with nitrogen
    • DIsolate it; take it to 25 mm Hg absolute
    Show the answer

    Answer: D Isolate it; take it to 25 mm Hg absolute

    Leaking parts are isolated from non-leaking parts where possible. Non-leaking parts must still reach the normal table level.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  9. 9.Before opening a chiller that has been evacuated, what must the technician do?

    • AAsk the owner to sign a disposal statement form
    • BAdd a small nitrogen holding charge
    • CRun the purge unit for two hours
    • DVerify the required level has been reached
    Show the answer

    Answer: D Verify the required level has been reached

    Before the appliance or part is opened, the technician has to confirm the required vacuum was really reached.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  10. 10.Mei recovers R-123 from one chiller and wants to charge it into another chiller owned by the same university. What does the rule require?

    • AIt must first be reclaimed to the AHRI 700 standard
    • BIt may be reused without recycling or reclaiming
    • CIt must be destroyed
    • DIt must be recycled through a filter-drier twice
    Show the answer

    Answer: B It may be reused without recycling or reclaiming

    Recovered refrigerant may go back into the same appliance or another appliance of the same owner without being recycled or reclaimed.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances

  11. 11.A low-pressure chiller at 0 psig is open for a small repair, and the section cannot be isolated. What must the technician do with the openings?

    • ALeave them open to let moisture out
    • BBlow nitrogen through them
    • CFill them with oil
    • DCover them
    Show the answer

    Answer: D Cover them

    When isolation is not possible, openings in a pressurized low-pressure appliance must be covered during the repair.

    Source: eCFR: 40 CFR 82.156 Proper evacuation of refrigerant from appliances