How deep to evacuate
Every low-pressure appliance must reach 25 mm Hg absolute before it is opened for a major repair or disposed of. That is roughly 29 inches of mercury vacuum.
- The level is the same with recovery equipment made before or after November 15, 1993.
- Charge size does not change it: the 200-lb split only matters for high- and medium-pressure units.
- Recover all the refrigerant, liquid and vapor, and confirm the level is reached before opening.
- You may evacuate just the part being serviced if its refrigerant can be held in a system receiver.
Major and non-major repairs
A repair is major if it removes the compressor, condenser, evaporator or an auxiliary heat exchange coil, or leaves more than 4 square inches open for more than 15 minutes.
- Non-major repair, not followed by evacuating the chiller to the atmosphere: bring the chiller up to no more than 0 psig before opening, and cover openings if the section cannot be isolated.
- For refrigerants that boil at or below 85°F at atmospheric pressure (R-11, R-123), use heat only: controlled hot water or a device such as Prevac. Nitrogen is not allowed because it would have to be purged out later.
- For refrigerants that boil above 85°F (R-113), heat as far as you can, then nitrogen may finish the job up to atmospheric.
- Oil changes: no higher than 5 psig. Warming the oil to about 130°F first drives out dissolved refrigerant.
- Leaky chiller that cannot reach 25 mm Hg absolute without contaminating the refrigerant: isolate the leak, take non-leaking parts to the full level, and leaking parts as low as practical, never above 0 psig.
Recovery and recharging technique
- Take the liquid out first, then recover the vapor.
- Keep water circulating through the tubes, or drain them, while the refrigerant is pulled out. Falling pressure chills the refrigerant enough to freeze still water.
- After reaching the vacuum, wait a few minutes. A pressure rise means refrigerant is still boiling off from liquid or oil.
- When recharging, put vapor in first, then liquid, so the tubes do not freeze.
- Charge centrifugal chillers through the evaporator charging valve.
Equipment and refrigerant reuse
- Machines made from November 15, 1993 need certification by an EPA-approved testing organization; older ones count as certified if they reach the required level on a calibrated gauge.
- Follow the maker's directions unless they conflict with the federal rules.
- System-dependent equipment is not allowed on charges over 15 lb unless it is a permanently attached pump-out unit.
- Refrigerant can go back into the same owner's chillers without reclaiming; a new owner means it must be reclaimed first.
Common traps
- Assuming old recovery machines get an easier level. For low-pressure appliances it is 25 mm Hg absolute either way.
- Using nitrogen to reach 0 psig on an R-123 chiller. R-123 boils below 85°F, so only heat methods are allowed.
- Charging liquid into a chiller in deep vacuum. Start with vapor or the water in the tubes can freeze.
- Stopping once the liquid is out. The vapor must be recovered too, and a rising pressure after reaching the vacuum means the job is not done.
Key terms
- 25 mm Hg absolute
- Required recovery level for every low-pressure appliance, about 29 inches of mercury vacuum.
- Major repair
- Removes the compressor, condenser, evaporator or auxiliary coil, or leaves over 4 sq in open for over 15 minutes.
- 0 psig
- Atmospheric pressure; the highest pressure allowed when opening a low-pressure chiller for a non-major repair.
- Controlled hot water
- Warm water run through the tubes to raise refrigerant pressure without adding gas.
- Evaporator charging valve
- The usual point for charging refrigerant into a centrifugal chiller.
- Pump-out unit
- Recovery equipment permanently attached to a chiller; the only system-dependent equipment allowed over 15 lb.
- Reclaim
- Reprocess refrigerant to the AHRI 700 purity standard; needed when recovered refrigerant changes owner.